how can we calculate that how much capacitor is needed for
a system to increase the pf?
Answers were Sorted based on User's Feedback
Answer / dinesh lokhande
A simple formula will help to co-orelate power factor, KW
load, and Kvar (i.e reactive power) required.
kvar = KW (Tan Qi - Tan Qd) where,
Qi = Cos inverse pfi = Initial power factor angle
Qd = Cos inverse pfd = Final power factor angle
After calculating Kvar we can select no of capacitors
required by looking at capacitor catalog.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / iamdon
Before doing mathematical manupulaion,as expaines very well
by our answer poster Dinesh.
Lets understand this simple fact that the power factor
changes due to the variation in Reactive power only.With
the help of power factor, one can easily calculate Reactive
power(Q=P*tan(arc cos pf)). The difference between reactive
power at two power factors is supplied by capacitor.
Author :arbelectbit@yahoo.com
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / wasifkhan2010@yahoo.com
KVAR =KW(tanQ1 - tanQ2)
where
KW= load of installation
tanQ1 = current power factor
tanQ2= target power factor
in thisway we can calculate KVAR of capacitor that how much
KVAR have to be improved.
Is This Answer Correct ? | 2 Yes | 0 No |
There is even no need to calculate. We have these charts which give the exact kvar required to be installed if we only know the load in KW and present pF and PF required.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
You can use the formula KVA^2=KW^2 +KVAR^2
Is This Answer Correct ? | 1 Yes | 3 No |
What is difference between ball screw and lead screw.
for star delta connection,,why the contactor star not burn,when red,yellow and blue cable is looping.
2 Answers Mahindra Water Utilities,
What is industrial plc
why near the transformers, the Jelly(small white colored rocks)are poured.and what are conditions for that?
How will calculate the current rating (withstanding capacity)of alumunium and copper cables?
Convert a star connected network into a delta connected network.
What is the 415V AC Soft starter? Explain with an example?
what is the reasons for blowing fuse
TO operate transformers in parallel, vector symbol of the both should be same.If one transformer name plate is not there, how can we conclude that whether the transformer is having the same vector symbol or not?
Alternating voltage and current is which type of quantities?
How can we determine or find out the proper size of any cable if nothing is mentioned on it.Calculation of size in Sq.mm???
domine+aptitude test means?