Answer / dinesh lokhande
A simple formula will help to co-orelate power factor, KW
load, and Kvar (i.e reactive power) required.
kvar = KW (Tan Qi - Tan Qd) where,
Qi = Cos inverse pfi = Initial power factor angle
Qd = Cos inverse pfd = Final power factor angle
After calculating Kvar we can select no of capacitors
required by looking at capacitor catalog.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / iamdon
Before doing mathematical manupulaion,as expaines very well
by our answer poster Dinesh.
Lets understand this simple fact that the power factor
changes due to the variation in Reactive power only.With
the help of power factor, one can easily calculate Reactive
power(Q=P*tan(arc cos pf)). The difference between reactive
power at two power factors is supplied by capacitor.
Author :arbelectbit@yahoo.com
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / wasifkhan2010@yahoo.com
KVAR =KW(tanQ1 - tanQ2)
where
KW= load of installation
tanQ1 = current power factor
tanQ2= target power factor
in thisway we can calculate KVAR of capacitor that how much
KVAR have to be improved.
| Is This Answer Correct ? | 2 Yes | 0 No |
There is even no need to calculate. We have these charts which give the exact kvar required to be installed if we only know the load in KW and present pF and PF required.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
You can use the formula KVA^2=KW^2 +KVAR^2
| Is This Answer Correct ? | 1 Yes | 3 No |
WHY LINK NOT A FUSE IN AC CIRCUIT
What magnetic circuit is formed in berry-type constructions and why?
what is meant by 3rd hormonics ?
when we are going to higher voltage level in substations why we are using Sf6 circuit breakers instead of Vacuum circuit breakers.
How calculate the MTA in relay?
If my sfu is 64 Amp & its link is 32 Amp then at what amp.my sfu will trip???
What is maximum power transfer theorem?
what is meant by power factor ?
what is cause of static electricity? I experience shock when i touch metal equipment in a room ,furher check shows earth leakage showing 80ma at the DB near to the 400 MCCB?
how to give earthing in plain?
What is bandpass of a transformer?
The readings with a Multi meter are 15 Amps Phase Neutral 192,Phase Earth 194 and Neutral Earth 24 5 Amps Phase neutral 192, Phase Earth 153, neutral Earth 48
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)