Why generating voltage is limited up to 22kV?
Answers were Sorted based on User's Feedback
Answer / iamdon
The generating voltage is limited up to 22kV due to
following reasons.
1)At voltage greater than 22kV, it is not ecomomical to
design the insulation for generator.
2)With the increase in voltage,armature current increases
which causes more loss in winding.So temperature of winding
increases which in turn rise the temperature of machine.So
we need more efficient cooling technique which is again
uneconomical.
Techinacal data:
1)5 degree increase in temperature reduces the life of
insulation by a factor of half.
2)20 degree increase in temperature reduces the insulation
resistance by a factor of half.
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / surendra
1. due to insulation cost.
2. for high voltage generation flux shuld be more for const
freq. thtwhy size of m/c become large which is not
economical.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gurucharan singh
As we go higher voltage level we to provide more insulatio
at generator winding. This increase the normall winding
working temperature indirectly cost of manufacturing.
Further higher temperature reduces life cycle of winding.
It alway preferred to limit generator winding voltage up to
22KV.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / s.arul
1) In generator voltage increased as well as increase the
winding insulation thickness.
2) so generator stator core size will be large.
3) In generator size also large.
4) Increase the cost of generator.
5) to transport the generator some problem will come.
Is This Answer Correct ? | 0 Yes | 0 No |
circuit breaker work alone during fault condition or need any relays ?
Types of circuit breaker
Can any body explain the operation system of MVWS(May be related to water and fire hydraunt system)?
Discuss about gear cutting machines.
transformer test
Can any body tell me about INNER SHUNT COMPOUND MOTOR diagram?
WHERE IS THE LIGHTING ARRESTER SHOULD BE PLACED IN DISTRIBUTION LINES?
why capacitor bank shorted by resistance ( 3 terminal )
explain 100 percent and 95 percent earth faults
in ct secondary one terminal is connected to earth why?
what is 33 /11kv transformer bdv
is it necessary for 200 kva transformer to have marshaling box and cu plate earthing for neutral