what is 33 /11kv transformer bdv
Answers were Sorted based on User's Feedback
it is a step down transformer, input is 33kv and output is
11kv
| Is This Answer Correct ? | 45 Yes | 7 No |
Answer / abhishek goyal
If u ask about BDV Value oil it should be minimum 40KV AS
PER IE STANDARDS. BUT IN INDIA WE MAINTAIN APPROX 50-60KV.
| Is This Answer Correct ? | 29 Yes | 5 No |
Answer / dharmesh
For new Tranformer 33KV/11KV Break Down Voltage(BDV) should
be more than 50KV......
| Is This Answer Correct ? | 22 Yes | 1 No |
Answer / parvinder kumar
For 33kv we needs a value above than 45 kv .Bdv value
| Is This Answer Correct ? | 14 Yes | 4 No |
Answer / k.prakashchandra
Did you mean bdv of oil in 33/11KV tr? It is 30 KV minimum
| Is This Answer Correct ? | 16 Yes | 8 No |
Answer / yogendra singh
that is stepdown transformer&we can use in ht supply
| Is This Answer Correct ? | 11 Yes | 6 No |
Answer / ramesh
This the step down transformer application
In 33/11kv
HV side is 33kv & LV side is 11kv
the connection is Delta To Delta in both HV And LV side
| Is This Answer Correct ? | 9 Yes | 6 No |
air condition capacity for masjad having 50feet in circal and 35 feet high
show the physical connection and phasor diagrams of 1: DZO 2: Yd1 3: DZ6 4: Yd11 5: YZ11
I have two power supply.a)govt. power b)Captive power.3 phase load connected inside factory.when source change govt. source to captive some motor rotate reverse. Is phase sequence changes when if off & on?If I off generator & on it again is it possible to get changed phase sequence??
what is the significance of tan&delta and how it performed in power transformer
WE know that for Inductor X=2pifL,In DC f=0,then X=0 so,V=IX=0;But In the DC excitation of rotor of AC generator,DC motor field coil which coils are inductor so why does not applying DC voltage short the rotor coil of AC generator and field coil of motor?If it would then DC source might be damaged but it is not happened. Why does the strand conductor of Electrical power transmission line make twist?
On a 6 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 42 AH). What Shall be the current rating of DC MCB ?
0 Answers TNEB Tamil Nadu Electricity Board,
what is mean by dual digital protection in the relay field?
does meager test perform on lightning arrester ? if doesn't then why ?
The insulation resistance of a cable can be measured by
what is phase voltage and line voltage? in line voltage how 415v is obtained?
reason of capacitor failure or low voltage in alternator wtih 10kva dgset
what is the principle of operation of tungstun bulb ??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)