If Two Generators are working parellel in a network and
suddenly the field of one Generator get weakened What will
happened if there is no reverse power relay fixed in that
Generator panel????

Answers were Sorted based on User's Feedback



If Two Generators are working parellel in a network and suddenly the field of one Generator get we..

Answer / g.bhardwaj

If two generators are working in parallel & no reverse
power relay installed then during weakened of field of any
gen set,definetly sick gen set work as a induction motor &
other gen set trip due to overload.

Is This Answer Correct ?    7 Yes 0 No

If Two Generators are working parellel in a network and suddenly the field of one Generator get we..

Answer / m.k.k

field weakened generator will run as induction motor

Is This Answer Correct ?    7 Yes 3 No

If Two Generators are working parellel in a network and suddenly the field of one Generator get we..

Answer / nishad

If there is no reverse power relay fixed, then it
definetely work as synchronous motor. if it work as the
same, it will affect the present network, because

1, It will draw the current from the other & will trip the
particular network system.

2,Already both generator working in parellel.so if one fail
the full load of the system will be the responsible of
working one. that's why it'll trip by over load.

3, If that field weaked generator work as a motor, it
defenitelt affect the primover ( Diesel Engine / Turbin)
there will be a chance of break down if it don't stop.

IF any another answer pls welcome>>> Nishad

Is This Answer Correct ?    1 Yes 1 No

If Two Generators are working parellel in a network and suddenly the field of one Generator get we..

Answer / lankesh

what you ment by field weakening Assuming field voltage is
reduced and another gen is having enough capacity, the weak
field gen wil deliver less reactive power as the mechanical
energy supplied is not reduced continue to deliver active
power

Is This Answer Correct ?    0 Yes 0 No

If Two Generators are working parellel in a network and suddenly the field of one Generator get we..

Answer / k.prakashchandra

Less excitation?. Then the generator will continue share the
load at leading power factor resulting in higher armature
current as the prime mover is still running and the terminal
voltage of the Gen is reduced.If this current exceeds the
set value ,Gen will trip on OCR which does not allow for
very low pf.

Is This Answer Correct ?    0 Yes 0 No

If Two Generators are working parellel in a network and suddenly the field of one Generator get we..

Answer / k.jeyvelraja

The weaked field get another set zero so that particular
gen worked not agenerator

Is This Answer Correct ?    0 Yes 2 No

If Two Generators are working parellel in a network and suddenly the field of one Generator get we..

Answer / raju pohane

if in running condition one generator field wdg became weak
that time this generator will go in field weakening
position and speed will suddenly high and generator will
trip on over speed due to tripping in one generator, load
will shift on another generator and if there will no span
for load in another generator it will also trip.

Is This Answer Correct ?    1 Yes 3 No

Post New Answer



More Electrical Engineering Interview Questions

at meter room 50 hrc switch installed,but there are not get earthing proper,so what happen?and 11kv transformer out put going in to hrc main 400a three nog each? so earthing is require for all switch? (some customer made earthing at there home.)

0 Answers   Ebrahim Textile, Siemens,


What is the ratio of true power to apparent power in an ac circuit?

0 Answers  


HOW TO CALCULATE THE HEAT AND LOAD OF LT-SUBSTATION WHICH CONTAINS 2*1MVA TRANSFORMERS,LT SWITCH BOARD,MLDB,ACB,BUSBAR,ETC...?

0 Answers  


how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating

0 Answers  


why transformer rating is mentioned in kva?

1 Answers   JK Electric Works,






What is static Device & Mechanical device? Is transformer a static device?

5 Answers   ABB, Emco,


what is ph test in coolent cheking

2 Answers  


in power generator normaly voltagr betwween esth to neutral is 0 but my work place generator show the volatge is 60v any body know why? thanks

0 Answers  


Why computer humming sound occurred in ht transmission line?

0 Answers  


what is the concept of star delta starter?

7 Answers  


draw the block diagram of fire alarm?

0 Answers  


What is milivolt dop test in Busducts? What is its significance & procedure to do the test?

0 Answers  






Categories
  • Civil Engineering Interview Questions Civil Engineering (5074)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4444)
  • Electrical Engineering Interview Questions Electrical Engineering (16594)
  • Electronics Communications Interview Questions Electronics Communications (3915)
  • Chemical Engineering Interview Questions Chemical Engineering (1092)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (214)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (258)
  • Instrumentation Interview Questions Instrumentation (2986)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (123)
  • Power Plant Engineering Interview Questions Power Plant Engineering (170)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (0)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1377)