If Two Generators are working parellel in a network and
suddenly the field of one Generator get weakened What will
happened if there is no reverse power relay fixed in that
Generator panel????
Answers were Sorted based on User's Feedback
Answer / g.bhardwaj
If two generators are working in parallel & no reverse
power relay installed then during weakened of field of any
gen set,definetly sick gen set work as a induction motor &
other gen set trip due to overload.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / nishad
If there is no reverse power relay fixed, then it
definetely work as synchronous motor. if it work as the
same, it will affect the present network, because
1, It will draw the current from the other & will trip the
particular network system.
2,Already both generator working in parellel.so if one fail
the full load of the system will be the responsible of
working one. that's why it'll trip by over load.
3, If that field weaked generator work as a motor, it
defenitelt affect the primover ( Diesel Engine / Turbin)
there will be a chance of break down if it don't stop.
IF any another answer pls welcome>>> Nishad
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / lankesh
what you ment by field weakening Assuming field voltage is
reduced and another gen is having enough capacity, the weak
field gen wil deliver less reactive power as the mechanical
energy supplied is not reduced continue to deliver active
power
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
Less excitation?. Then the generator will continue share the
load at leading power factor resulting in higher armature
current as the prime mover is still running and the terminal
voltage of the Gen is reduced.If this current exceeds the
set value ,Gen will trip on OCR which does not allow for
very low pf.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.jeyvelraja
The weaked field get another set zero so that particular
gen worked not agenerator
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / raju pohane
if in running condition one generator field wdg became weak
that time this generator will go in field weakening
position and speed will suddenly high and generator will
trip on over speed due to tripping in one generator, load
will shift on another generator and if there will no span
for load in another generator it will also trip.
| Is This Answer Correct ? | 1 Yes | 3 No |
What is the minimum setting in REF relay because i am facing some problem whenever power resumes after power failure my transformer is tripping because of REF trip. I am using CSPC make numerical relay(DIP switches). Now setting is 15 percentage. What is the reason for this triping. I sm waiting for answer
what is multiplying factor of a energy meter connected with a CT ratio of 600/5 and voltage at 415 volts.
what is the use of Reactive power in power system?
What is the operating range of voltage and current in grid supply in India?
how fault in an electric system is detected & hw protection of equipments is done ?
difference b/w bus bar and tie line?if possible explain with eg:
HOW TO REDUCE POWER PLANT AUXILIARY POWER CONSUMPTION?
we have an energy meter in a capacitor bank panel, So should we consider it's readings as energy consumption on daily basis. (when capacitor bank doesn't have any energy losses)
What is lc oscillator?
Application wise, where we should use AC motors and where we should DC motors?
how to calculate the change over time for star delta starter for different KW motor?
what are advantage and disadvantage of zener diode?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)