my question is that....few days ago i had installed a three
phase motor starter for an electric saw.the motor will run
and make the hydraulic pressure which will be goes to
pressure cylender by up and down lever.two number of
limitswitches are also installed on cylinder for safety of
motor.now when the arm of cylinder reaches to the upper or
lower limit it will cut the motor's line.and motor will be
stop.now wana know that what will i do that motor runs
continue after the limitswitch cut it down but it shold not
be made any pressure.pls answer me in brief.
Answers were Sorted based on User's Feedback
The motor is driving a hydraulic pump.Install a relief valve
set at the correct pressure in your hyd system where the pump
can perform its task but when the piston reaches the top the
pressure build up will be too high and the excess pressure is
released through the valve, the limit switches wont be
necessary any more.the pump will be running all the time.
| Is This Answer Correct ? | 0 Yes | 0 No |
c0ntr0l its up and d0wn s0len0id valve thr0ugh limit switc..
| Is This Answer Correct ? | 0 Yes | 0 No |
There should be some way to vent the excess pressure built by the motor. So first of all you should have a pressure gauge or sensor to read the pressure. Then you should have either a re-circulation line in the system or vent valve to channel the excessive pressure. When the hydraulic pressure reaches a set limit the re-circulation valve should open and channel the excessive pressure back to the tank/reservoir. In this way you can keep the motor constantly on without causing damage to system.
| Is This Answer Correct ? | 0 Yes | 0 No |
how is efficincy of the transformer is predermined
Can any one know what are the symbols at the down (below) the analog ammeter??? there are 4 symbols which are they ?????
how is differential relay working in transformer.comparison with generator defferntial relay
How much current can a 3-1/2 core 100 mm wire carry?
3 Answers Epitome, Focus, Focus Energy,
1 Kva = How many HP
Which are Electrical componet and Electronics componet??
Is there possible to Test Transformer for Overfluxing Capability. Or is there any firm who does Overfluxing Test on Transformer?
what is breaking capacity
Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..
why high speed tripping relay will be used in tripping circuit why not normal relay
Write the difference between OCB,VCB ?
Which of the following connection is best suited for 3-ph, 4 wire system A delta-delta B star-star C delta-star D star-delta
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)