my question is that....few days ago i had installed a three
phase motor starter for an electric saw.the motor will run
and make the hydraulic pressure which will be goes to
pressure cylender by up and down lever.two number of
limitswitches are also installed on cylinder for safety of
motor.now when the arm of cylinder reaches to the upper or
lower limit it will cut the motor's line.and motor will be
stop.now wana know that what will i do that motor runs
continue after the limitswitch cut it down but it shold not
be made any pressure.pls answer me in brief.
Answers were Sorted based on User's Feedback
The motor is driving a hydraulic pump.Install a relief valve
set at the correct pressure in your hyd system where the pump
can perform its task but when the piston reaches the top the
pressure build up will be too high and the excess pressure is
released through the valve, the limit switches wont be
necessary any more.the pump will be running all the time.
| Is This Answer Correct ? | 0 Yes | 0 No |
c0ntr0l its up and d0wn s0len0id valve thr0ugh limit switc..
| Is This Answer Correct ? | 0 Yes | 0 No |
There should be some way to vent the excess pressure built by the motor. So first of all you should have a pressure gauge or sensor to read the pressure. Then you should have either a re-circulation line in the system or vent valve to channel the excessive pressure. When the hydraulic pressure reaches a set limit the re-circulation valve should open and channel the excessive pressure back to the tank/reservoir. In this way you can keep the motor constantly on without causing damage to system.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is power factor? whether it should be high or low? why?
1- What is the Polarization Index number be good for 15KV 3c#500MCM electrical cable? 2- Can I use the IEEE Std 43-2000 to perfom the PI test? Thanks
Is there any Electrical supervisor license which gives permit to work whole India rather than individual state??
33kv substation lay out details & line to line & line to earth measurements
If 22 KV HT line, Current transformer is 25/5 then how to calculate multiplying factor.
Why does inductive loads consume KVARs?
what is the best way to start a 15 KW motor for pump star-delta or direct on line ? and from how many KW i must use direct on line ?
When we synchronize the Generator BKR with TIE BKR then Gen BKR is hold but TIE BKR is Tripped on Non directional over current but when TIE BKR is Syn. with Gen. BKR then no fault occur so what is the problem
why buchholz relay installed in inclined position
why celing fan is running in anti clock wise and table fan is running in clock wised?
What is the basic working principle of Tri vector meter?
how to calculate the input current in singel phase and 3phase supply to 5kva ups
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)