my question is that....few days ago i had installed a three
phase motor starter for an electric saw.the motor will run
and make the hydraulic pressure which will be goes to
pressure cylender by up and down lever.two number of
limitswitches are also installed on cylinder for safety of
motor.now when the arm of cylinder reaches to the upper or
lower limit it will cut the motor's line.and motor will be
stop.now wana know that what will i do that motor runs
continue after the limitswitch cut it down but it shold not
be made any pressure.pls answer me in brief.
Answers were Sorted based on User's Feedback
The motor is driving a hydraulic pump.Install a relief valve
set at the correct pressure in your hyd system where the pump
can perform its task but when the piston reaches the top the
pressure build up will be too high and the excess pressure is
released through the valve, the limit switches wont be
necessary any more.the pump will be running all the time.
Is This Answer Correct ? | 0 Yes | 0 No |
c0ntr0l its up and d0wn s0len0id valve thr0ugh limit switc..
Is This Answer Correct ? | 0 Yes | 0 No |
There should be some way to vent the excess pressure built by the motor. So first of all you should have a pressure gauge or sensor to read the pressure. Then you should have either a re-circulation line in the system or vent valve to channel the excessive pressure. When the hydraulic pressure reaches a set limit the re-circulation valve should open and channel the excessive pressure back to the tank/reservoir. In this way you can keep the motor constantly on without causing damage to system.
Is This Answer Correct ? | 0 Yes | 0 No |
What is the diff. between single compression and double compression gland
from which formula we select a capacitor rating?
Ac generato how produce power I need for camplet defination
why circuit breaker closing time is always higher then tripping / opening time.
effect of decrease in excitation?
anybody can give the voltage value for 1M ohm
hw the cable size can be calculated when we have watss, volts, pf, i need the forula
How a generator is positioned in a hydroelectric power plant?
how we can measure the dc current instead of clamp meter ?
Auto transformer starter gives the same effect as star/delta strater if its turn ratio = A 0.5 B 0.67 C o.66 D 0.577
Why the Petrol Guns in the Petrol bunk are earthed?
How to calculate the efficiency of Turbo Generator(Alternator) in general....?