pls give proper discription of selection of transformer
based on particular load.
Answer / bala_vlsi
first u finalized the connected loads and u will consider
diversity factor for individual loads . after this
calculation u will have some load in kw .
now u will convert to KVA
KW/ POWER FACTOR = KVA
Now you can select the suitable transformer for your
desiarable loads
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the importance of creepage distance in disc insulators
What happen to alternator if prime mover fails?
Where should the lighting arrestor be placed in distribution lines?
What is the knee point voltage of CT-100/5,15VA,5P20 ?
how to calclate fault level
What are the various types of rotor used in the alternators?
what is power factor?
why the supply power frequency is 50hz in india? where as it is 60hz in US?
we have a 2000kva step down transformer at our site. The HT side is charged from 22000V. So the primary current will be 52.48A. So why the HT breaker(SF6 ABB) is rated of 1250Amps ?
in the directional overcurrent and earthfault protection,normally we are setting the angle 45 deg lead for phase fault overcurrent and -45 deg lead for earthfault fro forward direction.but both the fault are operating on the same angle region only.why?how the relay will response?
What is difference between Ac Voltmeter And Dc Voltmeter ????
Define pole pitch?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)