pls give proper discription of selection of transformer
based on particular load.

Answer Posted / bala_vlsi

first u finalized the connected loads and u will consider
diversity factor for individual loads . after this
calculation u will have some load in kw .
now u will convert to KVA
KW/ POWER FACTOR = KVA
Now you can select the suitable transformer for your
desiarable loads

Is This Answer Correct ?    1 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

solar energy light efficiency & disadvantages?

1552


CAN CU XLPE/PVC CABLE BE USED INPLACE OF LOW NOISE SCREENED CABLE? KINDLY GIVE REASONS

1402


Difference between megger test equipment and contact resistance meter test instruments?

895


what is the difference between elcb and rccb ?

1769


why core is useful for a transformer ?and also in its operation ?

1570






can indirect loading be called as phantom loading?

1549


300m long and 30kw inductive loade 3phase supply how many size cable required

992


if sf6 gas low in gis what will happen

372


What are Contactors? How they works and what its highest rating?

1532


As a electrical engineer.. what are the basic norms should follow in transformer oil testing.. 1.What is the Electrode type? 2.How long time you will give for oil testing?

3081


What is the formula for calculating the Instantaneous Short Circuit & overcurrent for any breaker

1455


What is the function of probe in cro?

635


Explain the laying procedure and laying depth of submarine/subsea power cable for 220/400KV system? Also available cable diameter?

1677


What is power factor why we should maintain the power factor unless what will happen

1249


can i use 2000/5A Clamp meter to measure HT cable

1555