Answer / vithal k.
Power plant capacity is in MW means ultimately its in terms
of Amps, current and in PF.
Whereas DG is there in KVA means in terms of voltage and
current.
PP is directly connected to Grid and hence directly come in
to the picture with System inductance.. where as DG will
have bounded load and no more Inductive load is there
compared to Grid and hence negligibly considered as 1 (PF=1)
Ultimately in KW terms PF came out of picture and hence DG
rating ar3e normally in KVA.
| Is This Answer Correct ? | 13 Yes | 3 No |
Answer / rajsekhar mahapatro
All dg are rated in KVA but as other conventional power plants in kw because the dg's are local power plants they have to generate their own active and reactive power as well. But in modern power plants they are used to generate only the active component of power but not the reactive power, the reactive power required by the load is generated locally by using capacitors and other arrangement.So they are raked in KVA and KWs.
| Is This Answer Correct ? | 6 Yes | 8 No |
Answer / remodeen
MOSTLY POWER PLANTS ARE RATED SUCH THAT 210 MW., 600MW.,,
58MW.,,
BUT DG SET ALSO SAME THING BUT RATED IN KVA OR MVA.........
| Is This Answer Correct ? | 3 Yes | 16 No |
How does the sensitive earth fault protection provided by cbct for motor can help in reducing the size of cable used to supply the motor?
There are 2 motors without name plate and terminal but one is DC motor and another is induction motor.How one can identify which one is DC and which one is AC motor?
why is a earth pit 10 ft usually? And, what should be the distance betweeen two earth pit?
at what condition restricted earth fault relay will act?
What happens when the power factor is leading and its disadvantages.
what is feeder bay?
what is apparant power and reactive power
I am new guy as an electrical engr. in a 100MW HFO based power project. I am in operations division. I have noticed from last few days, my supervisor sends the last 24 hours energy generation calculation to my plant manager. I have noticed, he calculated last 24 hour's generated energy differences in KWH then he multiplied it with a multiplying factor 960. for example: total difference =2.685 KWH*960= 2577.6 MWH. but he does not not know what is multiplying factor 960?? can anybody explain it??
what is the effect of leading power factor
3 Answers Aurobindo, R L Steels and Energy,
what is difference between bus coupler and auto transfer switch
0 Answers Dubai Properties Group,
why do we provide metallic enclosure to bus duct and then ground it?
All the socket in a room become very hot, the Wall was also became very hot and the earth conductor also became live, what in your view might be the possible causes?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)