Explain the Term in CT Name Plate – Class: 5P10
Answers were Sorted based on User's Feedback
Answer / chola
CT error 5P10 It means .10 times of current fiows as per Ct
ratio the error will be 5%.
Is This Answer Correct ? | 14 Yes | 0 No |
Answer / mriganka das
Class 0f CT : 5P10.....
It state that if there 10 times current of plug setting
flows through the primary, there would be +/- 5 % error may
take place in the secondary side of the CT.
So 5 is the tolarence or accuracy class & 10 is the
accuracy class limit factor.it is denoted by the symbol
Eeta.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / s c budhiraja
this relates to ct meant for protection purpose.5p stands
for class of ct which means the current error at rated
primary current is 1%(+or-)and 10 mean that this ct will be
reasonably accurate upto 10 times the rated primary current.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / pravin
15 VA 5P 10
accuracy limit factor = 10
accuracy class = 5P
accuracy power = 15 VA
Is This Answer Correct ? | 1 Yes | 0 No |
It defines tat, at 10 times (During fault condition) of the
rated current of CT the accuracy shall be +/-5%.
for more, plz refer is-2705 part-1 to 4, ETD-34.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ganesan.n
5P - Accuracy Class
10 - Composite error rate accuracy limit primary current (%)
Is This Answer Correct ? | 1 Yes | 8 No |
1 ph induction motor winding priniple and connection diagram?Similarly for 3 ph induction motor?Full description
What is the type of earth fault protection used in battery? explain.
why we used servo motor insted of inducation motor?
What is the function of induction motor when low voltage is apply.
Why in ESP Positive earthed
a 50hz motor to give 60hz whats happening in motor.what happen the motor.
trasformer ratting
what is surge impedance loading?
only three phases are coming in step down tranformers.how to get neutral?
what is power factor ?
Define demand factor?
What is the capacitance values of 132,220,400 & 765 kV current transformer