Explain the Term in CT Name Plate – Class: 5P10
Answers were Sorted based on User's Feedback
Answer / chola
CT error 5P10 It means .10 times of current fiows as per Ct
ratio the error will be 5%.
| Is This Answer Correct ? | 14 Yes | 0 No |
Answer / mriganka das
Class 0f CT : 5P10.....
It state that if there 10 times current of plug setting
flows through the primary, there would be +/- 5 % error may
take place in the secondary side of the CT.
So 5 is the tolarence or accuracy class & 10 is the
accuracy class limit factor.it is denoted by the symbol
Eeta.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / s c budhiraja
this relates to ct meant for protection purpose.5p stands
for class of ct which means the current error at rated
primary current is 1%(+or-)and 10 mean that this ct will be
reasonably accurate upto 10 times the rated primary current.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / pravin
15 VA 5P 10
accuracy limit factor = 10
accuracy class = 5P
accuracy power = 15 VA
| Is This Answer Correct ? | 1 Yes | 0 No |
It defines tat, at 10 times (During fault condition) of the
rated current of CT the accuracy shall be +/-5%.
for more, plz refer is-2705 part-1 to 4, ETD-34.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ganesan.n
5P - Accuracy Class
10 - Composite error rate accuracy limit primary current (%)
| Is This Answer Correct ? | 1 Yes | 8 No |
What is difference between Electrical & Electronic Device?
7 Answers AZ Engineering, Vodafone,
what is negative phase sequence
Please tell me the power flow from pmg to main rotor of an alternator (Including AVR unit)?
What is the difference of grounding and earthing?
What is the technical name of minute currents that i have been produced in moving electrical objects?
1.what is the basic difference between surge arrestor and lightning arrestor and where we use it. 1.what is the difference between metal oxide without gapped lightning arrestor and with gapped lightning arrestor
when we are going to higher voltage level in substations why we are using Sf6 circuit breakers instead of Vacuum circuit breakers.
how can we calculate ct ratings ?its any formula ?
how to calculate lux level in out door (yard lighting) please expalin with a example
A 10 MVA, 66KV, 50Hz, Y-connected 3-phase alternator has synchronous reactance of 0.635 Ù. It is working at full load at 0.8 lagging p.f. condition. Find torque angle, neglect armature resistance.
requirements for making parallel operation of Uninterrupted power supply
What is the safety protection? Name the protections of Transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)