Explain the Term in CT Name Plate – Class: 5P10
Answers were Sorted based on User's Feedback
Answer / chola
CT error 5P10 It means .10 times of current fiows as per Ct
ratio the error will be 5%.
| Is This Answer Correct ? | 14 Yes | 0 No |
Answer / mriganka das
Class 0f CT : 5P10.....
It state that if there 10 times current of plug setting
flows through the primary, there would be +/- 5 % error may
take place in the secondary side of the CT.
So 5 is the tolarence or accuracy class & 10 is the
accuracy class limit factor.it is denoted by the symbol
Eeta.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / s c budhiraja
this relates to ct meant for protection purpose.5p stands
for class of ct which means the current error at rated
primary current is 1%(+or-)and 10 mean that this ct will be
reasonably accurate upto 10 times the rated primary current.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / pravin
15 VA 5P 10
accuracy limit factor = 10
accuracy class = 5P
accuracy power = 15 VA
| Is This Answer Correct ? | 1 Yes | 0 No |
It defines tat, at 10 times (During fault condition) of the
rated current of CT the accuracy shall be +/-5%.
for more, plz refer is-2705 part-1 to 4, ETD-34.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ganesan.n
5P - Accuracy Class
10 - Composite error rate accuracy limit primary current (%)
| Is This Answer Correct ? | 1 Yes | 8 No |
what is the name of oil used in transformer
11 Answers Energy Pack, Genco,
why we use 11 kv 22 kv and so on ?
What type of tranformer generaly at soft wares like capacity 2000 kva 1800 kva etc iam confused it CT or PT OR distribution tranformer
pls someone send me sample question papers along with the key.thanks in advance
why dimmerstate always connected in star connection? what will happen if it connected in delta?
What are the different protection systems takes place on control panel board?
what is the necessity of neutral in 3 phase system?
how to calculate the loss tangent of electrical cables
We store the d.c supply...then why can't we store A.c supply???
can we use the 110 v primary Tr 240 v secondary step up Transformer as reverse 240 pri 110 sec
Dear Friends, Need your help for connecting APFC panel, Quotation : I have 2 No’s 1000 KVA Transformers, both transformers are having separate APFC panels, ( Tr-1,400KVAR, TR-2,450 KVAR) Now I want to stop One transformer, present load is 650Amps, Max, So One transformer is enough, I have switched OFF TR-1, but PF is not maintaining properly, its 0.5, So now I want to connect TR-2 APFC also in TR-1 Loads, Can any one answer for my Quotation with drawing, how to connect TR-2 APFC panel in TR-1 Loads,
sir, plz tell me how much kvar capacitor required for 1000 amp or 500 Kw load ? what is the formula ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)