What types of testing in 11Kv Ht switchgeat during testing?
Answers were Sorted based on User's Feedback
Answer / n.venkidusamy
I think that site tests.ie. Pre commissioning Tests of
following.
1. Insulation Resistance Test for breaker and protection
and other cables
2. Check for spirit level
3. Mechanical spring charge test
4. Mechanical ON/OFF test
5. Electrical spring charge test
6. Electrica ON/OFF Both Local and remote Test
7. Contact resistance Test
8. opening and Closing timings tests.
9. Protection trip Test
10. Check for operation of Closing coil at 80% and Trip
coil at 70% rated Control D.C.voltage
Is This Answer Correct ? | 14 Yes | 0 No |
I belive you mean commisioning tests.
some of them are,
A)INSULATION TEST
b)contact resistance test
c)HV holding test
d)primary and sec injection test on the protection cct
e)transformers insulation, ratio test,vector group, insulating
oils dielectric tests.
f)cables insulation, phasing test
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / mriganka das
Transformer:
1)IR Test
2)Magnetising Current Test
3)Magnetic Core Balance Test
4)Vector Group Test
5)Ratio Test
6)Polarity Test
7)Oil Test (DGA,Dielectric Strength,Moisture content)
8)RLA test (Dirana, Thuran)
Current Transformer :
1) Ratio Test
2) IR Value Tset
3) Polarity Test
4) Knee Voltage Check
5) Winding Resistance Test
6) Back to Back Test
7) Tan Delta Test
8) High Voltage Test
Breacker Test:
1) IR Value Tset
2) Contact Resistance Test
3) Closing Tripping Timing Test
4) High Voltage Test
Isolator Test:
1) IR Value Tset
2) Contact Resistance Test
3) Closing Tripping Timing Test
4) High Voltage Test
5) Hot point Check ( in running condition)
Is This Answer Correct ? | 7 Yes | 1 No |
What are the significant parts of dc generator?
How many no. of earthing pits required for commisioning a new 320KVC DG Set????How????
what is meant by real power,active power,reactive power & apprent power ?please explain it?
diff between UPS and inverter?
What are the effects of adding a zero to a system?
'documenˁ
We are having a 2000KVA DG set. It trips with Over speed and Engne Hot when the mahine is stopped in full speed. How shall I analyse the block load and reverse power.Is the problem related to power factor. The machine which runs on this DG is having all Synchronous motors with incividual Drives.
how we can set the IDMT relay.
Even motor protection, why motor burn out ?
what is acceptance test in electrical engineering.
What are the symptoms of a bad PG card of a drive (inverter) esp. of Yaskawa Ac Drives (inverters) G7 ?
why core losses are affected with change in voltege in transformer?