Stepwise process of Northern grid failure in 2012!? (dont
copy paste from wikipedia)
Answer / mebin g mathew
According to the report, Some of the high voltage lines of
Northern Grid were under maintenance and hence the other
lines were highly loaded EVEN 400kv line was used to
compensate the power shutdown of 765 KV LINE. So the 400 KV
line was highly loaded. Due to this the, line tripped and
this worsened the condition load bearing problem for the
other line since all the power requirement came to other
lines. They also started tripping in power swing and some
relays even detected zone 3 tripping(false tripping).
When a huge load was released, the power plant had to shut
them down to protect the generators and other equipments in
plant. A power plant require hours to reignite and start the
production in full flex. And there was a panic to
immediately start production because all were shocked of
the incident.
So thus the norther grid was isolated from other region
grid. That led to a complete black out in North India.The
report ends with an interesting statement that this might
have happened due to hacking of powergrids PLC engineering PC.
Is This Answer Correct ? | 3 Yes | 1 No |
what is diffrence between MH LAMP and HELLOZEN LAMP
What are reasond for high wattage in single phase induction motors
What is the starting current of a motor?
what you mean swtchgear(electrical)
What is meant by reset level of the relay?
why restricted earth fault protection can not operate for phase faults??as there will be a current in secondary of ct,when a phase fault occurs!
what u meant of power plant?
In HI POT test what is reason for applying the AC VOLTS and DC VOLTS in different applications what is the nessesity for this ?
why active power is called as real power or working component.What is the exact function of active, reactive & apperent power.
Why design 150Hz in Exciter
in conclusion why we select you?
is it possible to step down voltage of single phase from a three phase sysem? explain