What types of testing in 11Kv Ht switchgeat during testing?
Answer Posted / n.venkidusamy
I think that site tests.ie. Pre commissioning Tests of
following.
1. Insulation Resistance Test for breaker and protection
and other cables
2. Check for spirit level
3. Mechanical spring charge test
4. Mechanical ON/OFF test
5. Electrical spring charge test
6. Electrica ON/OFF Both Local and remote Test
7. Contact resistance Test
8. opening and Closing timings tests.
9. Protection trip Test
10. Check for operation of Closing coil at 80% and Trip
coil at 70% rated Control D.C.voltage
Is This Answer Correct ? | 14 Yes | 0 No |
Post New Answer View All Answers
what is data block in plc ? How the values of data block are written and read by hmi ? what is the difference between function and function block ?
How to calculate the External Resistance required for 60HP slipring motor in case no any data of the Motor is available???
Which thing is maximum in RLC circuit at resonance a)power consumption b)inductive current c)capacitive voltage
Is there any guideline say about display of earthing value near to earth pit
what causes contact chatter when there is no demand on the air conditioning unit?
why sielent pole is used only in hydro generators and not in turbo generators
Why electrical power generation and transmission done in 3 phase system not more than 3 phase ?
What is a dominant pole?
Define peak time.
If we have to feed a housing complex having load 8MVA, than what would be the better option, either we first step down 33kv supply into 11kv & than 430v or we proposed no of 33/.44 kv transformer, also which option is economical?
what is the difference between capacitive and resistive voltage divider?
what is the clear formula to calculate cable size for a load
What is the function of retrip in busbar?
what does mean of RCT and STR in diffrential CT?
should %impedance be high or low in a power transformer? if so why?