why we are using DC supply for all protection relays, why
cant we use AC supply..???
Answer / n k singh
We can use AC also but additional shading ring must be
provided which gives sufficient phase displaced flux for
relay to be continuously on in negative half cycle of AC
supply also. In case of DC the flux is unipolar hence relay
will be on if DC is available.
| Is This Answer Correct ? | 5 Yes | 3 No |
why we are giving D.C. supply to field of an alternator, why can't we give the a.C. supply
what is synchronous speed.? if an induction motor is made to run at full load, then is this synch. speed too..?
What is the difference between solid grounding and impedance grounding?
what is 33 /11kv transformer bdv
How you calculating the 30 Hp 3 phase AC motor of power what size of cable is used for this motor?
750kva 11/415kv transformer having percentage impedence is5.64%. 11KV HV whose current 39.37A and 415V LV whose current 1043.43A.resistance is 2.5ohm. find no load loss and full load loss?
what happen to a dc series motor if it given as ac supply accidentaly
what is stper motor.what is its uses
Logic using 1 kV or 1,1 kV grade in house wiring Low voltage cable. Explain/suggest? some use 1kV and some prefer 1.1kV grade insulation low voltage cable why??
cable armor
how to syncronize two dg sets
pls tell me about ups internal connection & we have given only 3 phase supply to ups system how get 4 wire (R Y B N )
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)