Please provide me detail cable voltage drop calculation
Answer / arshadullah
Voltage drop for selected cable
Vd = mV * I * L/N * 1000
Where,
mV : milli Volt
I : CURRENT
L : LENGHT OF CABLE
N : NUMBERS OF RUNS
| Is This Answer Correct ? | 2 Yes | 0 No |
what is the principle of tubelight ??? what is the function of starter and choke ???
why we use post insulators in no ofstacks at substation for supporting equipment ? why we not use single post insulator
i need bhel question papers.
the single phase voltage is 230 volts and threee phase is 430 v.why three phase is not 660 v?
if a damaged 500kva transformer with %impedance 2.6 is replaced by two transformers of 250Kva with different % impedance will they be able to catter the load. what will be the ratio of load on the two transformers if the % impedance is in the ratio 1:2
If we want the fan to consume less electricity at low speed, what do we have to do?
what is scan time of PLC & in which factor scan time is decide
Why transformer rating is represent in KVA?
7 Answers Bhel, Sonalika, Usha Martin, Wipro,
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
how can we choose the size of road crossing pipe for power cables
how many typetesting of transformers?
what are the protecyion of transformer & generators
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)