why we use post insulators in no ofstacks at substation for
supporting equipment ? why we not use single post insulator
Answers were Sorted based on User's Feedback
Answer / rahul singh
In order to increase its creepage distance so that
recommended phase to ground clearance can be attained. Also
the helical shape/edges are provided in stacks to avoid the
accumulation of water in case of rainfall & mechanical
strength also increases in this design.
For 220kv Post Insultors - Creepage distance= 6125mm
For 132kv Post Insulators- Creepage distance= 3625mm
For 33kv Post Insulators- Creepage distance= 900mm
Thank you.
Rahul Singh
Electrical Engineer
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
To make transportation,packing ,manufacture and erection easier.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vishal ingle
above answer is correct. in short just for ease of handling
at all the levels.
| Is This Answer Correct ? | 0 Yes | 3 No |
Difference between DOL starter & star Delta Starter? And where the Dol starter used upto how much HP and whereas Star Delta vice versa?
DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF YES THEN WHAT ARE THE ACCEPTED R VALUE REQUIRED FOR SURGE ARRESTORS FOR VOLTAGE LEVEL 11KV, 33KV
haw to calculate resistance of induction motar
What is 100% protection of generator? Why 95% protection is used not 100%?
Tell me the reason of connecting domestic t/f primary in star or delta,and also secondary side.
In a transformer, the hysteresis and eddy current losses depend upon 1.load current 2.maximum flux density in core 3.type of lamination 4.supply frequency The correct statements are (a) 1 and 3 (b) 2 and 3 (c) 1 and 4 (d) 2 and 4
if we look on phasor of the transformer vaoltage is 180 oppsite at primary and the secondary so to improve a power factor is secondary should kept negative to improve it primary side means is -.90 became +.90 at other side
on what priciple transformer works on?
if our load in 3 phase circuit is 4000 amp. calculate the capacity of capacitor panel if line power factor is.80 .
how to decide the rating of the ct for 1500 kva transformer
When a square wave is applied to primary of a transformer then what will be output wave form of secondary ?
what is the effect of PF on alternator sizing?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)