Why transformer rating is represent in KVA?
Answers were Sorted based on User's Feedback
Answer / ramakrishna
Losses in transformer cuper losses & iron losses.cuper
losses depends on current iron losses depends on voltagge.
total losses depends on va not depend on phase angle b/w
voltage & current
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / sarbudeen
all the devices (execpt loads like
motor) diesel generators,
transformers, ups are rated in kva
only,
it saying that i can provide total
power (kva) and its ur problem
how u split it (kw+kvar)
depending on load u provided. But
i can give this amount of total
power (kva).
Is This Answer Correct ? | 4 Yes | 2 No |
Because the only thing which doesn't change both side is multiplication of voltage and current. So if any one can calculate the other side values if he have n1 : n2 ratio and any 1 value, ie voltage or current.
Is This Answer Correct ? | 0 Yes | 0 No |
A power transformer contains two main part –the windings-
copper or aluminum conductors insulated –and the magnetic
core.
Magnetic core requires an excitation current in order to
maintain the required magnetic field.
The excitation current depends on supplied voltage and if
the supplied voltage is over a certain limit the excitation
current presents a threshold and start to be very high.
This voltage is the rated voltage.
On the other hand, the conductor insulation rated
temperature is limited-according to insulation class-since
above this limit the insulation will be damaged.
The temperature arise depends of the current passing
through conductor and producing heat losses. These losses
depend only on the absolute value of the current and it is
not connected to the active load [kw=volt*current*p.f. then
the maximum kw it is when p.f.=1 then kw=kVA].
The product of voltage with current is measured in VA or
kVA=1000 VA or MVA=1000000 VA.
Is This Answer Correct ? | 1 Yes | 3 No |
As the transformer is not specified for a particular power
i.e active power or reactive power and the unit of acive
power KW and the unit of reactive power is KVAR for that
reason transformer rating is represent in KVA.
Is This Answer Correct ? | 3 Yes | 5 No |
Answer / lokanna.adekar
Losses of transformer depends upon voltage
Is This Answer Correct ? | 0 Yes | 2 No |
Can anybody tell the formula to calculate temparature rise in the cable with respect to current?
We are using 4 MVA transformer and we provided 2 separate earthing pit for Body and 2 separate earthing pit for neutral, can we connect separate body earthing pit to other earthing pit (Equipment earthing)?
I have a one P.F meter in my factory showing 2 phase leading and one phase lagging then what is my actual P.F.
how many winding in the single phase transformer?
which is dangerous AC or DC?
What is LOP Sensor in DG??????
What is the similarity and what is the difference between relays and PLC?
What is the advantage of AC supply?
how does a liquid starter reduce the starting currents?
how to calculate compresor capacity?
How many loops can be provided in a circuit as per IS rules.?
what is the term of desruptive voltage
5 Answers Bhel, Energy Infratech,