i dont think. In all places ,motors are used to start by
starters only.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / dani jindal
who told you dat starters r not used in an industry. we
always go for a DOL (direct on line starter)which includes
type1 r type 2 protection co ordination n people ve above
replied i thnk about star delta starter which nt at all
depends upon the rating of the motor, as we knw the motor
drawas around 6 to 8 times the full load current during
starting if dat effects ur other equipment connected to
same line then go for star delta starter, if ur
distributiom Transformer is capable enough to withstand dat
surge inherited go for DOL starter.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / arun_sekar_1986
No for low rating of motors starters may not required.But
for higher rating starter is Mandatory. To reduce high
starting current starter are used while starting in step by
step it is used.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / suresh
In industries they normally use it.Ofcourse it may not be
required for motor of lower ratting say below 1kW or around
it.
| Is This Answer Correct ? | 2 Yes | 1 No |
oh/...well frnd...u must have seen at any small industries.
they must have used be cos of cost.U can never find in any
standard company.it may happen if its very low rating motor
like up to 0.33kw.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ravikumar.g
With out starter in the industries motor are not starting.
If the starte is having a safty for the motor.
If the single phases some times will start directly.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dharmaraj
mostly lower rating not used for starter upto 1 kw more
then we should be used for starter
| Is This Answer Correct ? | 0 Yes | 0 No |
What is the method for testing the differential protection stabilty in generator? When the time of starting What will happen if differentail protection connection wrong means?
how to calculate current when LT supply 415v fed to HT Motor 6.6kv and 1120kw.
Why CT secondary is grounded?
what is the working principle of Brushed alternator ? without exictation how we can give dc supply to rotor ?
Why reactive power is needed in a power system? How is it being absorbed or delivered by alternators? For reactive power control we are changing excitation but reactive power absorbing or delivering related to stator. How these two are interlinked? i want a detailed explanation with necessary expressions and figures?
If stator & rotor of a 3-phase induction motor have different no. of poles, will the motor run or not??
why ohms law does not obey semi-conducters?
What happens when the power factor is leading and its disadvantages.
In 90 kva alternator that produce the output voltage is 115(p-n),200(p-p) at 1500 rpms means what ampere it produced ?
What is CVT and what is relation with wave trap?
What do you mean by boost voltage in case of battery charger?
What is the exact load current needed for a place which has 100nos of bulb of each 100w?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)