1.Can anybody explain Why starters are not used for motor
starting in industries?
2.
Answers were Sorted based on User's Feedback
i dont think. In all places ,motors are used to start by
starters only.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / dani jindal
who told you dat starters r not used in an industry. we
always go for a DOL (direct on line starter)which includes
type1 r type 2 protection co ordination n people ve above
replied i thnk about star delta starter which nt at all
depends upon the rating of the motor, as we knw the motor
drawas around 6 to 8 times the full load current during
starting if dat effects ur other equipment connected to
same line then go for star delta starter, if ur
distributiom Transformer is capable enough to withstand dat
surge inherited go for DOL starter.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / arun_sekar_1986
No for low rating of motors starters may not required.But
for higher rating starter is Mandatory. To reduce high
starting current starter are used while starting in step by
step it is used.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / suresh
In industries they normally use it.Ofcourse it may not be
required for motor of lower ratting say below 1kW or around
it.
Is This Answer Correct ? | 2 Yes | 1 No |
oh/...well frnd...u must have seen at any small industries.
they must have used be cos of cost.U can never find in any
standard company.it may happen if its very low rating motor
like up to 0.33kw.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ravikumar.g
With out starter in the industries motor are not starting.
If the starte is having a safty for the motor.
If the single phases some times will start directly.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dharmaraj
mostly lower rating not used for starter upto 1 kw more
then we should be used for starter
Is This Answer Correct ? | 0 Yes | 0 No |
What is the previous name of Cox's Bazar
electrical resistance in human body?please dedails quick. mail.psrinivasan20@yahoo.com
We use ACB in LT and VCB in HT.But if we use VCB in LT and ACB in HT that what will be the effect on the system or any power range?
How to checked frequency drive output voltages?
whow we find out dc motor field aur armature resistance
what is the pulse and audio frequency transformer? what is different between induction regulators and tap changing transformer?
Why Neutral Busbar CT & transformer neutral CT connected with phase CT in Restricted Earth Fault?
What should be the Sandwitch type Al. bus bar capacity for 2 M.W.Gen. set, having continuous full load current- 3463 Amps,ambient temp.- 50 Deg. C., Required temp. raise-20 deg.C., it will run 24 hrs, 365 days on full load, required highly reliable.
an electric bulb or lamp can operate on ac and dc, if yes then why
sir can you operated Transformer on frequency from that for which is design?
For backup batteries connection,which method is best? series or parallel ?
WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying to a lighting & power socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8 times of Ir , tsd = 0.5 sec( I2 t off). Sometimes this MCCB is tripping .But no trip in DB MCB. Can anybody tell me reason ? From where i can know about the MCCB settings?