What is the exact load current needed for a place which has
100nos of bulb of each 100w?
Answers were Sorted based on User's Feedback
Answer / karthik
for single phase, P=VIcos0.
When P=100W, Icos0=P/V.
Icos0=100/230.
for 100 nos, Icos0=100*100/230
=43.48A
if cos0=0.9, I=48.3A
Is This Answer Correct ? | 11 Yes | 2 No |
Answer / errol
assuming a 230V power supply:
I=P/V where P= 100W x 100pcs = 10,000watts
Total current, I, therefore is 10,000W/230V = 43.48A. The power factor is 100% bearing in mind that bulbs are resistive loads.
Is This Answer Correct ? | 7 Yes | 0 No |
what is working of Master trip relay ?
What is the phase relationship between the primary and secondary voltages of a transformer?
which fault current is maximum: 3 phase short circuit, LG, LL or LLG?? why?? in one of the problems that i have solved, 3 phase short circuit current on an unloaded generator came out to be less than the LG fault current. can anybody please explain why.
On what basis no of earth pits are to be decided either for transformers or for equipment?
which type of ICs can be used in resonant power converter?
why the earth conductor in top of the tranmission line ?
A separately excited dc motor having 2 ohm armature resistsance draws a current of 10A and torque developed is 20 Nm under rated field condtion. the speed of the motor under the rated field condtion , when it is connected to a 100V DC source and delivering 10Nm torque....
What is the breakdown voltage?
where lt & ht capacitor used
IN 1000kva transformer where the oil and winding temperature sensors is connected
How will A Medium voltage circuit breaker(11 kV voltage level) operate under short circuit fault condition whether It is having short circuit release like Low voltage circuit breaker or relay should be given?
the single phase voltage is 230 volts and threee phase is 430 v.why three phase is not 660 v?