What will be the total current for 300kva UPS if it runs on
40 to 45 percent load. Is there any formula for to
calculate the exact load.
Answers were Sorted based on User's Feedback
Answer / pratheesh
We can calculate the total output current of a 300kva ups.
P=√3*V*I*CosΦ
Where P= Output power of UPS here 300000VA
V= Output voltage of UPS ( I hope this is a 3 phase
415 volts UPS)
I= Output current. (We need to calculate)
CosΦ= Powerfactor of the load. Varies depends the
nature of load(Inductive, Resistive or
Capacitive. We can assume this value is as 1
because we dont know the powerfactor, nature of
load.
So I= P/(√3*V*CosΦ)
= 300000/(1.73*415*1)=Approximately 420A per phase(if
the load distribution is balanced on each phase)
So, If the UPS runs on 40 to 45 percent load, it will take
around 170 to 190 Amps on each phase.
Is This Answer Correct ? | 14 Yes | 8 No |
Answer / thowsif_emerson_csm team
For 300 KVA the Full load Current=KVA*PF,
i.e 300x.8=240000 Watts.
we know in 3 Phase Circuits,
P=1.732x V x I x Pf,
I=P/1.732xV x Pf,
I=240000/1.732 X 440 X 0.8,
Full Load Current, I =240000/609=394 Amps,
The Load Current @ 40% is 394*.40=158 A(Total Load Current).
The Load Current @ 45% is 394*.45=177 A(Total Load Current).
So load current at 40% Load is 39*.40=15.6 A/Phase Amps.
Is This Answer Correct ? | 11 Yes | 6 No |
Answer / panindra polayadi
p=vI
where p for poore
v for vada
I for idippu
when we apply 40 to 45% load entteammo poore will blast
at that time vada will reduce idippu will be constant it is
newton,s fourth law after somedays newton,s fifth law will
be come beware
Is This Answer Correct ? | 0 Yes | 4 No |
hi this toufik here. i am doing my b.e.degree.now i am in final year and supposed to do a project in this year so i thinking to control the buchholz relay using software base means checking the status of transformer oil using microcontroler, plc or scada. so can i do so...??? alz suggest me...
What are the fire Estingushers use in electrical fire?
what is formula for calculate thermal overload in new numiricalrelay( not in bimetal relay)?
How to test lightning Arrester?
Is it possible to make 0.75KW motor earthing from MCC panel by using the 1.5 SQMM, 4 core cable, means 3 core for 3 Phases & 1 core for Earth terminal?
Explain about p.t?
how much current (in MW)can be carried max. through S/C dog & Panther Conductor ?
what is use of thermistor ?
defination of generator
what happens if DC earthing and AC earthings are shorted?
what is the reason for indication of light in the earth lamps of main switchboard.if there is an earth why does one lamp get dim and the other two bright.
what is pilot wire protection? wer is it using?