Answer / t. eswara rao

Capacitors are used for compensating the inductive reactive
power in the system and bring the power factor to the unity.
But the question is what is problem if we connect them in star?
If we connect them in star , and any capacitor fails ,
it momentarily shorts the supply voltage and raises the
voltage levels across the remaining capacitor banks
connected in the remaining phases. This may lead to destroy
the other two capacitor banks also.

Is This Answer Correct ?    32 Yes 10 No

Why we connect the capacitor in Delta?if we conect in Star what will happen?..

Answer / k.ravindran

When connected in delta, the voltage on each capacitor will
be the phase voltage.
When connected in star, the voltage on each capacitor will
be the phase voltage divided by root of 3.
If the capacitors are rated for the available phase
voltage, then they can be connected either in delta or in
star.

Is This Answer Correct ?    28 Yes 10 No

Why we connect the capacitor in Delta?if we conect in Star what will happen?..

Answer / faraz ahmed

Wye connected capacitors connected to motors are not
appropriate because they are ungrounded and thus present a
potential difference on each phase of the capacitor which
contributes to the over-all deterioration of the capacitor.
As can be seen in fig.1 below, the failure of any one cell
of a Wye connected capacitor presents an unbalanced load to
the motor. This will effectively destroy the motor due to
unbalanced voltage, temperatures.
Example: If you have a 100HP motor and an unbalance of 5%,
this will cause a power loss of 25%. (100HP – 25% = 75HP).
If the motor was loaded to 85%, the motor now becomes
overloaded. The motor would run 113.5% overloaded, therefore
overheated and will eventually burn out.
Unprotected Wye connected capacitors should not be used for
Power Factor correction. The unbalance protection required
for this type of application is more costly than the
capacitors themselves and therefore not included with Wye
connected capacitors.
Wye connected capacitors do not circulate harmonics and thus
are much more vulnerable to failure due to harmonics.

Fig.1 - The total capacitance for the example above with a
failed cell would be 5kVAR
Delta connected three phase capacitors are more friendly to
the electrical environment. They not only provides
capacitance to each phase but also provides no voltage
unbalances (harmonics).
If a capacitor cell should fail for any reason in one phase,
we are going from a closed delta to an open delta
configuration and in this instance the voltages on each
phase stays the same (see fig.2 below). Failure of a
capacitor cell would only mean a drop in the kVAR on the
circuit. In other words, a 30kVAR delta connected three
phase capacitor with a failed cell would provide 20kVAr to
the electrical system instead of 30kVAR.
Delta connected capacitors unlike the Wye connected
capacitors are able to circulate harmonics currents within
the delta circuit. By doing so it reduces the harmonics on
the electrical system.


Fig.2 - The total capacitance for the example above with a
failed cell would be 20kVAR

Is This Answer Correct ?    10 Yes 0 No

Why we connect the capacitor in Delta?if we conect in Star what will happen?..

Answer / miguel

kvar will be less.

Is This Answer Correct ?    3 Yes 1 No

Why we connect the capacitor in Delta?if we conect in Star what will happen?..

Answer / pravin m sonwane

in medium voltage Delta connection or star ungrounded is
mostly used because of

1)Harmonic current is circulated in delta loop, hence no
damage to system

2)Across capacitors phase voltage is present.

3)more efficient configuration than other like star, star
grounded, star ungrounded, double star neutral may or may
not be isolated, double star with neutral grounded.

4)No zero sequence or third harmonic currents can flow in a
star-connected capacitor bank. Additionally, where one
series group per phase is used, the individual capacitor
fuses should be capable of interrupting the system
short-circuit phase-to-phase fault current.

5)The greatest use of A-connected banks is at 2400 V, since
this is the lowest standard capacitor voltage rating.

6)As zero sequence or third harmonic is absent, less
protection to bank is required. hence less costing in such
capacitor configuration.

Is This Answer Correct ?    2 Yes 0 No

Why we connect the capacitor in Delta?if we conect in Star what will happen?..

Answer / sahil>m

Cy=3 C delta so value of cap will go high

Is This Answer Correct ?    4 Yes 7 No

Why we connect the capacitor in Delta?if we conect in Star what will happen?..

Answer / sunil guru

if we convert the power from delta to star then the power
received is very less and not sufficient for compensating
purpose and making power factor at utility but while getting
star to delta power the power received is high and
advantageous.....

Is This Answer Correct ?    2 Yes 8 No

Why we connect the capacitor in Delta?if we conect in Star what will happen?..

Answer / mira

because capacitors in delta provides reactive power 3 times
than that connected in star..such as in capacitor banks.

Is This Answer Correct ?    5 Yes 15 No

Why we connect the capacitor in Delta?if we conect in Star what will happen?..

Answer / rabindra

the capacitance of the capacitor in case of star is 3-times
that in delta connection,so i think the capacitor may
destroy.

Is This Answer Correct ?    6 Yes 33 No

Post New Answer

More Electrical Engineering Interview Questions

How to calculate capacitor bank size at a load 800kVA.

0 Answers  


how i decrease the neutral to ground voltage , thats i read 7v on my digital meter.i dont know about my earth pit.

2 Answers  


what will happen while giving 2 phase supply to 3 phase motor

5 Answers  


how to revers the direction of single phase motor

0 Answers  


Why Earth pits are inter connected

8 Answers   Airtel, Taj Group,






why dc source used for HV breakers and Relays operation?

2 Answers   Cethar,


why r use the wave taper in the substation ?

2 Answers   L&T,


Why the transformer rating is denoted in VA rating why not in KW

7 Answers  


what is meant by cbct elr?

3 Answers  


What is the BS(British Standard)code for 11kv motor

1 Answers  


Can you tell me more about pu systems (per unit systems )calculation in large power systems? how to get the base for voltage and power in generator, transformator and transmission lines?

0 Answers  


What are the different pre-commissioning tests that are performed on the distribution transformer, power cable and switchgear (11kv)?

1 Answers   Hitech, Reliance,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)