Is it possible to make 0.75KW motor earthing from MCC panel by
using the 1.5 SQMM, 4 core cable, means 3 core for 3 Phases &
1 core for Earth terminal?
Answers were Sorted based on User's Feedback
Answer / najam sultan
For earthing we don't need to use 4 cores, only a single core is enough for earthing.And 1.5sqmm single core cable is enough for earthing of 0.75 kW motor.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / avd
Yes it can be done.Do not worry for fault level because it
will be greaty reduced due to lowersize cable.But make sure
you have installed earth fault protection device to isolate
incase of earth fault.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mukesh
For motor we need to use 3 cores, only a single core is
enough for earthing.And 1.5sqmm single core cable is enough
for earthing of 0.75 kW motor and double earth is
requirements for whereas 3 phases is used as per rule.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jyotiranjan sahoo
Yes it can use 1.5 sqmm cable of earthing for that motor but in Indian standard we must be use another body earthing
| Is This Answer Correct ? | 0 Yes | 0 No |
Specify the crystal frequency required for an 8085 system to operate at 1.1MHz
at which places we use 6.6KV Transformers and Motors
one KVAR takes how much amps, and how to add power capacitors to electrical panels, for example if one of the MCC drawn 800amps means how much KVAR required
what is the difference between energy efficient and high efficiency motors
Why single phase induction motors are not self starting ?
What happen to the transformer if the OLTC frequently used for lower and raise occured 50times daily?
If i have two 3000 kW motors and the whole facility requires a 10 MVA transformer. What would be better installing two 5 MVA transformers(one for 1 motor ) or just a single 10 MVA transformer for both of them. Give reasons for your answer.
what is bus pt and what is the function of it
How Size of Busbar is determined for a particular load.
How may I enrol or get admission to your program?
Please tell me the formulaes while designing a substation for power Calculations in designing a 33 KV Substation?????
What is the difference between single point and double point bonding. please kindly detail about bonding of cables.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)