How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva
oil type transformer system?
plz provide step by step calculation
Answers were Sorted based on User's Feedback
Answer / divay chadha
3core-185 sq. mm
Calculation:-
Current at HT = (1500 x 1.4)/ (33*1.732)
Is This Answer Correct ? | 267 Yes | 142 No |
Answer / s.srinivasan
Generally HT cable sizing is not done based on the full
load current of the equipment but based on the prospective
fault level. For a 11kV network, generally it shall not be
less than 150sqmm XLPE.
Fault level at 11kV(furnished by respective EB)=100 MVA(say)
Details on EB's fault level can be obtained from EB.
Therefore fault current= 100*1000/(SQRT(3)*11000)
= 5.25 kA
Short circuit current rating (for 3-sec duration)of HT 11kV
XLPE cables with Alu conductor is as below:
95 sqmm: 5.16 kA
120 sqmm: 6.51 kA
150 sqmm: 8.14 kA
Is This Answer Correct ? | 138 Yes | 29 No |
Answer / j.kesavan
please slect your cable in 11kv py side how much current
check first after you slect your ht cable.
Is This Answer Correct ? | 93 Yes | 42 No |
Answer / neeraj tyagi
simple for 11kv
Amp in HT= kva*1000/ 1.732*11000
= size for 78 amp HT XLPE 3 core 95 mm2 higher side.
Is This Answer Correct ? | 92 Yes | 51 No |
Answer / gb
11kv----13 amps on primary side
1500 kva 1.4 = 2100 amps on secondary
Is This Answer Correct ? | 43 Yes | 29 No |
Answer / madhu mohan
First calculate the current of primary side(HT) and derate the cable by atleast 0.7.
Eg:1500*1000/(1.732*11000)=78.73A
Current I after Derating =78.73/.7 =112A (0.7 if laid on the trays or value will vary if buried in the ground).
Cable equivalent to rating has to be selected.
Now Short circuit withstand capacity (sq. of I X t in sec) has to be checked from the cable catalogue.This value of cable should be higher then SC withstand capacity of the ground usually it is 50KA.it less go for next size and finalise.
Is This Answer Correct ? | 32 Yes | 24 No |
Answer / sairaj
90 Sq.mm Al Ar XLPE cable is sufficient. But as per statutory norms for 11kV, 185 Sq.mm Cable is considered.
Is This Answer Correct ? | 15 Yes | 9 No |
Answer / murugan
How to select different types of Transformer KVA rating,
with matching cable size in Primary and secondary..?
100kva TR = cable size with full load amps rating
150 kva TR = ???
250 kva TR = ???
500 kva TR = ???
750 kva TR = ???
1000 kva TR = ???
The cable size
95 sqrmm
120 sqmm
150sqrmm
185 sqrmm
240 sqrmm
300 sqrmm
400 sqrmm
500 sqrmm
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / engr. md n h shabuj
S=(Ish *√t)/K
=(10.49*√1)/0.143
=73.35
=75Rm cable
Ish =P/ (√3*V* % of Z)
= (1500*10^3 )/( √3*11*10^3*7.5%)
=1049A
Ish =1049*10=10490A=10.49KA
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / saad yar khan
Where can I get the chart for selecting HT cable based on 1500KVA i.e 78Amp
Is This Answer Correct ? | 0 Yes | 1 No |
the 230 value of voltage which is use in our home . is that value is rms, aerage or peack value of voltage?
How Calculat the Cable Sizing of HT/LT System & Explian by one Exampal?
What is the BS(British Standard)code for 11kv motor
why anti pumping relay is not given to tripping coil of the breaker? why only to closing coil?
A 400KVA ,50HZ TRANSFORMER IS TO BE OPERATED AT 50HZ.THEN KVA RATING OF THE TRANSFORMER?.
Which type of a.c motor is used in the fan (ceiling fan, exhaust fan, pedestal fan, bracket fan etc) which are find in the houses ?
How to test REF relay testing for LV panel as per Kahramaa standard?
what are the main problems that happen in an emergency light and how to fix them ?
Would you recommend to replace all oil filled cables with xlpe cable for hv transmission with the current technolgy for xlpe cable?
for ac networks if the voltage wave form is V=Vm sinwt here the voltage Vm=230 for the frequency 50hz then the time period is 0.02 sec then for the time period 0.12 sec what is the voltage
what is negative d.c. voltage, why this voltage is used in base transciever station.
what is the pperating squvance in transmission line for circuit braker, isolater & earthing switch.