what are the difference between protection class CT and
Class PS CT
Answers were Sorted based on User's Feedback
Answer / siddharth agasti
class ps ct is a protection class ct.it is used for
differtial proction,distance proction.
Is This Answer Correct ? | 47 Yes | 4 No |
Protection class CT are 5 p10 and 5 p 20 and PS class ct
are used where neutral point is available such that star
conneccted secondary of Transformer and alternator ,it is
used for differential protection.
Is This Answer Correct ? | 25 Yes | 9 No |
Answer / shivaji mangalagiri
all the protection cts like over current
relay and earth fault relay of transformer,Alternator and
HT motors are having core 1 and core 2 options. CLASS PS
type is used only for differential protection purpose of
transformer,Alternator and
HT motors only. and this type of cts are available only in
PAIR SCHEME (PS) AND their turns ratios,
impedances, VA burdens, knee point etc all these critical
parameters are exactly matched with each other.
Is This Answer Correct ? | 18 Yes | 4 No |
Answer / s.rajasekar
the saturation point between the ps is higher than
protection class & metering.and the accurracy is also
higher then protection CT. It has highly efficient so it is
mosly used in sofasticated protections ( REF,DIFF,DISTANCE )
Is This Answer Correct ? | 9 Yes | 1 No |
Protection class is ued in protection like over current
relay and earth fault relay of transformer,Alternator and
HT motor.PS class is used in DIfferential protection like
transformer,Alternator and HT motor.
Is This Answer Correct ? | 13 Yes | 6 No |
Answer / manoj
Both Protection class and class PS CTs are used in
protection circuits only. As someone mentioned earlier,
class PS CTs are special CTs used in all types of
Differential Protetion scemes. they generally come in pairs
and they are special in sense their turns ratios,
impedances, VA burdens, knee point etc all these critical
parameters are exactly matched with each other.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / satheesh
the saturation point between the ps is higher than
protection class & metering.and the accurracy is also
higher then protection CT. It has highly efficient so it is
mosly used in sofasticated protections (DIFF,DISTANCE )
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / mauhammad yasir abdul-rub
The Difference Between protection class and metering class
is mainly of saturation, the saturation values of protection
class is higher as when fault occur protection CT must not
get saturated as high current flows and metering CT can be
saturated as when fault occur metering is not necessary,
accuracy is also a factor but not the main factor
Is This Answer Correct ? | 8 Yes | 6 No |
Answer / selvam.s
Protection CT:
this type of CT can be used for protect the breakers.
5P10,5P15 & 5P20 are called protection current transformer
1) 5 means accuracy of sensing fault current
2) 'P ' means "protection"
3) 10,15 & 20 means ( no.of times ( 10,15 &20 ) X actual
current rating of breakers .
PS CT:
PS means protection special current transformer.
this type CT can be used for differential protection in
transformer & in alternator.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / r.suryamuthuraman
if any fault occurs core needs to saturated for protection
of ct.because ct secondary ckt will goes to relay current
coil .secondary ckt of ct will having resistance and
current.to avoid saturation want to decrease the burden of
ct.ps means special protection having high accuracy than
other class
Is This Answer Correct ? | 0 Yes | 1 No |
What is CBCT ,why and whereit is used?
Why we call cable rating in SQ.mm.If it is 240 SQ.mm how much the diameter possible?is there any calculation ?
if the back emf eqution for dc motor EB=(QPNZ/60A) THEN what is the value of A for PMDC MOTOR OR how can dicide the value of "A"
By just seeing a transmission tower, how can we knew the voltage it carries..?[110kv, 220kv, 400kv...]???
WHY IS THE EARTH FAULT CURRENT ALWAYS LESS THAN THE NORMAL CURRENT??
What is core CT & it's function?
What is a Single Phase and Three phase Power? How it will be converted or transformed into another form?
need to make a report. Need to choose a 3phase induction motor. Load conditions motor will operate in : Maximum Load: 30 Kw Speed: 2950 rpm Ambient temp: 20 cent Supply voltage: 440V Frequency: 50Hz need to look for the safety factor when choosing the motor, went through catalouge found a few, but dont know how to choose the safety factor allowing an extra load something above 30 KW to avoid any harm.
Why generation voltage in thermal power plant is between 11kv to 33kv?
What is the Harmonics??????????
kindly tell me how the load on generator increase by just increasing the fuel of prime mover, as if for exampple 20 MW gen set is synchronized the load ramps from zero to 20 MW gradully and during this procress only fuel of prime mover increases. Which thing determines the load on generator with respect to fuel
raleigh method