How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva
oil type transformer system?
plz provide step by step calculation
Answers were Sorted based on User's Feedback
Answer / rasel-amie
HT Cable select, its depend of incoming capacity of feeder
line. say feeder capacity 100 MVA SO Calculate current I=
100*100/11*1.73=5.25kA. So we can select of HT Cable for
minimum short ckt current carrying capacity of minimum 5.2kA.
| Is This Answer Correct ? | 10 Yes | 14 No |
Answer / er.rupam dwivedi
A=kva x 1000/1.732x ht voltage=ht cable selection
| Is This Answer Correct ? | 2 Yes | 6 No |
Answer / govind bisht
Assume PF of transformer is .8.
rating of transformer=1500kVA=1500X.8=1200kW
V=433(3phase)
So that maximum current-
I= P/V*PF
=1200*1000/1.732*433*.=1600A
So cable size required if copper cable
1mm=4amp= 400sqmm(by consedering all factors)
For aluminium cable
1mm=2.5A=640sqmm
| Is This Answer Correct ? | 61 Yes | 109 No |
Answer / m.jagadeeshwar
for 11kv side current = kva*1000/1.732*11000
= 78.73 amps
for 78.73 amps 3 core 25 sqmm cable is sufficient
| Is This Answer Correct ? | 22 Yes | 84 No |
what is a power factor?
0 Answers MPWU Kiribati, Thermo,
What will happen if we give the 3 phase supply to the rotor of slipring induction motor?
Fantio of tranformer
why in India it is maintained for exactly 50HZ frequency, why it is not that 49Hz,why it is so?
Can clean earth cable be considered as low current cable
difference between ground,neutral and earth?..
How to convert a two phase power into a three phase power in induction machine?
IN THE CASE OF AN ELCB, IF THERE IS ANY UNSTABILITY BETWEEN PHASE AND NEUTRAL IT MAY TRIP. BUT MY QUESTION IS WHEN A LOAD IS CONNECTED IN BETWEEN P AND N, THE LOAD CONSUMES SOME POWER AND THERE IS A DIFFERENCE IN NEUTRAL WITH RESPECT TO THE PHASE. THUS ACCORDING TO ME, THE ELCB WILL AUTOMATICALLY OPERATES WHEN EVER THE LOAD CONSUMES-- I KNOW IT IS WRONG. BUT THE SOLUTION IS?????????
Resistance of low voltage side of transformer compared to high voltage side is A less B equal C more D depens on design
How do you commission a power Transformer?
why -48 volts dc used in telecommucation
advantage of motor design on higher power factor . normally motors are designed for .8 power factor. what is advantage of designing at .88 power factor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)