How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva
oil type transformer system?
plz provide step by step calculation

Answer Posted / uday

1500kVA X 0.8 PF = 1200Kw = 1200000W

P=RT3 V I COS fi

SO, P
I = -----------
RT3 x V x COSfi

1200000
I = -----------------
1.732x1100x0.8

= 79 A

Now take cable table and select the suitable xlpe cable.

Uday

Is This Answer Correct ?    46 Yes 51 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what should be correct gas pressures to be a 1.5 ac unite

1078


Can 33kva/415v transformer be run underground? If the answer is yes why and if the answer is no why?

1177


how we can do the insulation on secondary of ct explain and so that tan delta will within limit

1454


what is the transformer turn ratio formula and give some examples?

1933


What the difference between ac and dc inductor an capacitor

1736






what are problems caused by the pdu in rack server

1460


How to test the Secure Elite 440 Multi function meter working condition.

1614


What are the reasons for the parallel operation of transformers?

626


for 4 MVA , 33K.V/6.6K.V transformer. secondary side the connected load is 3000H.P. What is the rating of capacitor bank to be insttaled.

2151


how much excitation voltage required to generate 1mw power?

1605


What is the purpose of using busbar mounting fuse?

1605


how many stairs have you climbed while you were coming

1702


WHY IN AC DRIVES,INPUT PHASE CURRENT SHOW UNBALANCE?

1727


What will happend if given Vfd out put to step up transformer

1250


What difference between ref protection and differential protection ?

1341