How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva
oil type transformer system?
plz provide step by step calculation
Answer Posted / uday
1500kVA X 0.8 PF = 1200Kw = 1200000W
P=RT3 V I COS fi
SO, P
I = -----------
RT3 x V x COSfi
1200000
I = -----------------
1.732x1100x0.8
= 79 A
Now take cable table and select the suitable xlpe cable.
Uday
Is This Answer Correct ? | 46 Yes | 51 No |
Post New Answer View All Answers
what should be correct gas pressures to be a 1.5 ac unite
Can 33kva/415v transformer be run underground? If the answer is yes why and if the answer is no why?
how we can do the insulation on secondary of ct explain and so that tan delta will within limit
what is the transformer turn ratio formula and give some examples?
What the difference between ac and dc inductor an capacitor
what are problems caused by the pdu in rack server
How to test the Secure Elite 440 Multi function meter working condition.
What are the reasons for the parallel operation of transformers?
for 4 MVA , 33K.V/6.6K.V transformer. secondary side the connected load is 3000H.P. What is the rating of capacitor bank to be insttaled.
how much excitation voltage required to generate 1mw power?
What is the purpose of using busbar mounting fuse?
how many stairs have you climbed while you were coming
WHY IN AC DRIVES,INPUT PHASE CURRENT SHOW UNBALANCE?
What will happend if given Vfd out put to step up transformer
What difference between ref protection and differential protection ?