How to calculate HT XLPE CABLE for 11 kv / 433 v , 1500 kva
oil type transformer system?
plz provide step by step calculation
Answer Posted / rasel-amie
HT Cable select, its depend of incoming capacity of feeder
line. say feeder capacity 100 MVA SO Calculate current I=
100*100/11*1.73=5.25kA. So we can select of HT Cable for
minimum short ckt current carrying capacity of minimum 5.2kA.
Is This Answer Correct ? | 10 Yes | 14 No |
Post New Answer View All Answers
Define what is difference between fuse and breaker?
from generating station If 400v LT line length is 1000m how much voltage is drop and how do i calculate it? which cable will be use for this line?
Do closed loop systems require manual input?
why normally Generator rating are between 11Kv to 22Kv?
Earth bits close or open. Which is correct
i am gng to visa interview this july i have 4 backlogs gre 1010,toefl 75,pls give me the tips pls pls
how to measure the current by compact digital equipment with dislay which fit inside any equipment
Where can I get Iidian straderd specifications for electrical items or works in web? please help me.
How to checked frequency drive output voltages?
Write the analogous electrical elements in force current analogy for the elements of mechanical translational system.
What are the factors influence the choice of an electrc drive?
WHAT IS SHORT CIRCUIT STRENGTH OF 100 AMPS MCCB?
Dear friends I want to design busbar for1600 kva transformer(i.e2100 amps) what are all the factors to be considered before selectinga busbar what are all the standard sizes of busbars what is the formula for finding current of copper and aluminium busbar
how line turns ratio changes in 3 phase with change in connection
1600 KVA ka transformer hi aghar lt side par 800A aur voltage 420 ho to HT side ki cable ki rating keya ho gi?