what is diffrence between neutral and earth wire
Answers were Sorted based on User's Feedback
Answer / kunal
An Earth wire is used to provide a path for leakage current
in case the body of an equipment is in touch with a naked
portion of live wire whereas a neutral wire is there to
provide a closed loop to the flow of current in an
equipment.
The neutral is earthed at the Distribution transformer
secondary side.
| Is This Answer Correct ? | 121 Yes | 11 No |
Answer / anand
Neutral is a return path to complete the electrical
circuit. It is originated from transformer star point.
Earthing is connected to the panel or equipment to protect
the equipment & human life when leakage occurs.
| Is This Answer Correct ? | 68 Yes | 4 No |
Answer / manish tailor
neutral define as a closed path of electical ckt having
zero potential.and earth wire is a protection path of
electical ckt.
| Is This Answer Correct ? | 59 Yes | 20 No |
Answer / ashish chopra
neutral wire is there to form closed path of current
earth wire is there for the protection of equipment from
the leakage current and also provide ground path to leakage
currentand hence saves human life
| Is This Answer Correct ? | 36 Yes | 4 No |
Answer / rocky ram
An Earth wire is used to provide a path for leakage current
in case the body of an equipment is in touch with a naked
portion of live wire whereas a neutral wire is there to
provide a closed loop to the flow of current in an
equipment.
The neutral is earthed at the Distribution transformer
secondary side.
| Is This Answer Correct ? | 23 Yes | 5 No |
Answer / manveer
An Earth wire is used to provide a path for leakage current
in case the body of an equipment is in touch with a naked
portion of live wire whereas a neutral wire is there to
provide a closed loop to the flow of current in an
equipment.
The neutral is earthed at the Distribution transformer
secondary side.
| Is This Answer Correct ? | 14 Yes | 1 No |
Answer / sanket patil
UNDER HEALTHY CONDITION BOTH WIRES DONOT CARRY CURRENT.
EARTHING WIRE CARRIES LEAKAGE CURRENT AND AS ITS
RESISTANCE IS LESS(USUALLY<0.2 OHM UPTO THE POINT WHERE IT
IS EARTHED) IT PROVIDES ALTERNATE PATH TO CURRENT AS
RESISTANCE OF HUMAN BODY IS MUCH HIGHER( APPROX. 1000 OHM).
THE NEUTRAL WIRE MAY CARRY CURRENT UNDER UNBALANCED
CONDITIONS IN A THREE PHASE SYSTEM.
| Is This Answer Correct ? | 15 Yes | 7 No |
Answer / phani
neutral is used as a one of the point in potential
difference and another point phase.it acts as a closed loop
for the circuit.
earth wire is used to protect our body and equipment when
there is a contact with live wire.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / azhar
neutral which carry the un balanced current to the system
..and earthing provide the leakage current to the earth in
the electrical or electronics equipment...
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / nidit kumar
Neutral wire means not at a zero potential i.e it may be at
zero or at other potential.One can use this for reference
potential.
Earth wire is always at zero potential.Earth wire is always
use, for making the voltage of the matalic body at zero
potential i.e potential difference between metalic body and
earth becomes zero.
| Is This Answer Correct ? | 6 Yes | 2 No |
WHAT IS MEANT BY INSULATION CLEARANCE IN VACCUM?
defination of a.c filter
hoe to select the cable size in sq mm for certain load?
How to prepare electrical preventive maintenance plan & shedule of machine tools in manufacturing unit.
we have one oven for 12 zone we are installed ir lamp in oven we control load from thyrister and 0 to 5vdc so our zone no 8 getting bright in fraction of second so what we do.. Please answer
tan delta test of current transformer.
in DG synchronization system can i short R,Y,B- phase(DG-1) to R,Y,B Phase (DG-2), HOW IT WORK . WHAY WE NEED TO SYNCHRONIZATION.
which relay is better , instantaneous or IDMT relay .
Why we use Carbon & graphite mixxed brushes in the DC motor?
How to calculate capacitor bank value to maintain unity power factor with some suitable example?
whenever a squirrel or a crow gets tangled near the out put of the feild transformer there is a discharge of 440 volts of current through the neutral due to which my appliances blow up causing a huge bang.will the RCCB help in these conditions
what is reactive poower
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)