which relay is better , instantaneous or IDMT relay .
Answers were Sorted based on User's Feedback
Answer / karthik
for metering, protection all will be taken in one CT --only core will be varied in that CT
for measurement -1s1,1s2
for protection - 2s1,2s2
only one CT is used
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / biswaindu parida
In a substaion we use different ratio of CTs for different purposes. Such as 200/1 for metering 400/1 for another back up, 800/1 for protection like wise. So suppose if a fault comes say around of 1200A then the secoundary level current for different Cts will not be same.
Lets analyse them indivisually.
1) The 800/1 Ct will read it as 1.5A. For that we can simply use Over current relay and trip the breaker.
2) The 400/1 Ct will read it as 3A . here we can use IDMT relay.
As per its function it will sends trip command to the breaker as soon as possible...because here the time of trip is inversely proportional to the amount of fault current
3) But however in case of 200/1 CT, it will read it as 6A. If it is a metering CT then it should be protected 1st. because it has less saturation point as compared to protection or back up CT. So here we will use instantaneous relay so that it will trip suddenly when the fault current goes above some pre defined value.
| Is This Answer Correct ? | 0 Yes | 3 No |
if There is Short circuit in Power Transformer, what will happened to Buchholz Relay.?? How Buchholz Relay will respond.??
can we start mulitple 3 phase induction motors with common starter?
What are the types of excitation system?
In UPS, battery connections if parallel connection given, what will happen?
how snubber circuit works to protect switching devices?
Whata are the types of Cables?
what is the calculation formula for motor starting torque,running torque, running torque.
What are the reasons for AVR failure in LT DGsets ?
which model T or pie model is prefarable in power syatem
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
how many types of ratings are there of transformer
i want to know how to calculate the battery capacity based on the UPS . ex i want to run have one kva UPS Which should run 10 hours ? in that case how many batteries to be installed and what will be the AH Value .
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)