Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


If Solenoidal valve works in manual mode but not in Auto
mode. What should be the problem?

Answers were Sorted based on User's Feedback



If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?..

Answer / satishkumar

first, check the SOV coil is working or not and then check
the power supply from DCS to sov coil.

Is This Answer Correct ?    18 Yes 5 No

If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?..

Answer / raffi

Signal(Soft PB) for SOV to open in Manual and Auto are same (DO)
While your are running in AUTO. it is working with interlock/logic i.e feedback from other IOs

While in Manual mode you should press the SOV button to open after change the mode to manual

If it not working in AUTO then Check the malfunction of feedback signal IO card or carryout the loop checking for feedback signal to sort out the issue

Is This Answer Correct ?    8 Yes 0 No

If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?..

Answer / fellyc

Assume that both Manual Command (PB) and Auto signal comes
from the DCS ( Same DO).
If it works in Mamual Mode and not in Auto Mode, then check
the logic for an interlock or permissive.

Is This Answer Correct ?    3 Yes 2 No

If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?..

Answer / ganapathi s.b

First check DO out put came or not. if signal not come check Do module, if signal came then check sov coil Resistance value
either open or short.this is main problem of not working in Auto mode.

Is This Answer Correct ?    1 Yes 0 No

If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?..

Answer / raja

Need to be check the DCS I/O cart the DI cart digital output cart some time give fault signel the I/O cart malfunction

Is This Answer Correct ?    4 Yes 4 No

If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?..

Answer / sriram

Either manual mode u operate from dcs then the DO card is good. so check the interlock

Is This Answer Correct ?    0 Yes 0 No

If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?..

Answer / hansdas b.jaiswal

If you are operate solenoid valve with out load so please
connected it a power cylinder or actuator some time
solenoid valve not works in auto mode with out load.

Is This Answer Correct ?    0 Yes 0 No

If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?..

Answer / govarthan

whether card is not working sov not working in man mode also i think ter s an external interlock check it..

Is This Answer Correct ?    1 Yes 8 No

Post New Answer

More Instrumentation Interview Questions

please can anyone tell me in detail, what's mean by open loop and close loop?

6 Answers  


How to measure high frequency using thermistor

1 Answers   DRDO,


What is NAMUR standard and why its allways reletad with Sollenoid

2 Answers  


in split range control valve,two valve should be in two different line and that should have some distance,and we have only one positioner feed back link.so how we connect one feed back in two control valves?if you have picture please forward me.my email id kb.syamkumar@gmail.com

2 Answers  


THE OUTPUT OF A CURRRENT TRANSMITTER OR A PNEUMATIC TRANSMITTER HAS A LIVE ZERO?EXPLAIN

2 Answers  


i have 20 kw motor & my vfd drive capcity is 18 kw if possible to use 20kw motor on this vfd?

4 Answers  


how to use one 4-20mA signal for two indicater or controller & give necessary precaution.

2 Answers  


what is the difference between transmitter and converters?

9 Answers   Videocon,


How would i calibrate a new commissioned flow transmitter???

3 Answers  


Specify for Cables - Flame Retardant and Fire Resistant?

0 Answers  


what is the approximate cost of U tube manometer having range 1000mmwc to 1000mmwc?

1 Answers  


how to install the Ph and Conductivity analyser? is there are any procedures which has to be maintained.

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)