If Solenoidal valve works in manual mode but not in Auto
mode. What should be the problem?
Answers were Sorted based on User's Feedback
Answer / satishkumar
first, check the SOV coil is working or not and then check
the power supply from DCS to sov coil.
Is This Answer Correct ? | 18 Yes | 5 No |
Answer / raffi
Signal(Soft PB) for SOV to open in Manual and Auto are same (DO)
While your are running in AUTO. it is working with interlock/logic i.e feedback from other IOs
While in Manual mode you should press the SOV button to open after change the mode to manual
If it not working in AUTO then Check the malfunction of feedback signal IO card or carryout the loop checking for feedback signal to sort out the issue
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / fellyc
Assume that both Manual Command (PB) and Auto signal comes
from the DCS ( Same DO).
If it works in Mamual Mode and not in Auto Mode, then check
the logic for an interlock or permissive.
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / ganapathi s.b
First check DO out put came or not. if signal not come check Do module, if signal came then check sov coil Resistance value
either open or short.this is main problem of not working in Auto mode.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / raja
Need to be check the DCS I/O cart the DI cart digital output cart some time give fault signel the I/O cart malfunction
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / sriram
Either manual mode u operate from dcs then the DO card is good. so check the interlock
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / hansdas b.jaiswal
If you are operate solenoid valve with out load so please
connected it a power cylinder or actuator some time
solenoid valve not works in auto mode with out load.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / govarthan
whether card is not working sov not working in man mode also i think ter s an external interlock check it..
Is This Answer Correct ? | 1 Yes | 8 No |
can u briefly explain aboutan aryton shunt multirange DC ammeter?
a flow transmitter [range-0-400mbar] connected in process line. please explain me how to calibrate the flow transmitter , & how to do static error
Hi Friends i am going to write BARC written test by this month 20th (20-5-2008). So please if any body knows the details about this or having previous question papers pls mail me to kkumarei@gmail.com. For Suggestions give one message to 9962122264
1)why we are using mostly Ultrasonic Flow meters to measure flow, rather than Radar waves? 2)why we are using Ultrasonic waves and Radar waves to measure the Level?
What is the difference between Pressure Safety Valve and Pressure Relieve Valve, in what condition we prefer choose Pressure Safety Valve rather than Pressure Relieve Valve? and vice versa
give classification of transducer based on type of application
hi my name is rakesh patel i just complited my be in instrumentation & control now i am going to working as a validation engineer in a poject department so what is a scope in a future as a validation engginer ? what line is good for me can any bady give me complete solution please? your regard rakesh patel
what is interlock system and why we use of this?
how to convert digital signal to analog signal in plc
please send me hpcl placement papers
how to convert bar to mA?
what is shutoff dp? why is it important for selection of a control valve?