control valve in manual/auto mode huntting checked spring
tention also it is ok.positioner also good condition &
incoming inst air line also constant pr.kindly give us
correct answer?
Answers were Sorted based on User's Feedback
Please check following things:
1. To loose gland packing, due to tight packing, valve may hunt.
2.Check leakage from diaphragm.
3.May be seat or plug loose
4. Check cut marks at feed back linkages.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / gopalakrishnan.p
Kindly check the following thigs for betterment
1.Loop tune ur controller.(gain value,integral
time,derivative time).
2.Check the cable(connector side ..i,e may be loose
connection).
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ashish namdev
Kindly check these following :-
1. first check positioner link spring.
2. adjust link assembly.
3. adjust instrument air at valve specified pressure
through AFR.
4. check all parameters and settings in positioner.
5. give auto calibration command and calibrate it.
6. Tune your controller.(gain, PID controlling)
| Is This Answer Correct ? | 2 Yes | 0 No |
please check followings:
1-check gland packing if tight then may be loose.
2-If booster relay installed then check its equlizer valve
some time this valve called by-pass valve.The valve may
adjut to approprite position as hunting stop.
3-Check feed back linkage with touch any part of the body.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / imran
First check its feedback link spring if it is ok then
checked its feedback potentiometer by removing it from
positioner with meter.these r main causes that already i
faced.
| Is This Answer Correct ? | 0 Yes | 0 No |
how to use one 4-20mA signal for two indicater or controller & give necessary precaution.
What is negative range in transmeter?
why does a transmitter o/o signal starts from 3-15psi or 4- 20mA?
how to convert transmitter milliamps output to like temp,pressure etc.....
how to measured k type thermocouple temp.
Hi buddies! my name is sachin and i am working as a electrical and instrumentation engineer in a paper plant. right now i am facing a problem and if someone could help me it will be an immense pleasure to me. i am using AC 800M to synchronise DCS500 drives on paper machine and rewinder.communication is on PROFIBUS and we are using NPBA-01 module to link profibus to DC drives.But these days two of these drives are showing a error named FIELDBUS COMM.TIMED OUT and the drives get tripped.I have changed the NPBA module and PROFIBUS cable.So if anyone can do please help me out with this problem.I'll be highly grateful.
WHAT IS THE DIFFERENCE BETWEEN A TRANSMITTER & A SMART TRANSMITTER.
what is the input of digital counter during the the calibration time?
In the field and in the control room different power supplies if used How to handle the ground
what is a half wave, full wave, and bridge rectifer.
field bus transmitter calibration procedure tell me
How to calibrate Toxic gas detector?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)