Please check following things:
1. To loose gland packing, due to tight packing, valve may hunt.
2.Check leakage from diaphragm.
3.May be seat or plug loose
4. Check cut marks at feed back linkages.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / gopalakrishnan.p
Kindly check the following thigs for betterment
1.Loop tune ur controller.(gain value,integral
time,derivative time).
2.Check the cable(connector side ..i,e may be loose
connection).
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ashish namdev
Kindly check these following :-
1. first check positioner link spring.
2. adjust link assembly.
3. adjust instrument air at valve specified pressure
through AFR.
4. check all parameters and settings in positioner.
5. give auto calibration command and calibrate it.
6. Tune your controller.(gain, PID controlling)
Is This Answer Correct ? | 2 Yes | 0 No |
please check followings:
1-check gland packing if tight then may be loose.
2-If booster relay installed then check its equlizer valve
some time this valve called by-pass valve.The valve may
adjut to approprite position as hunting stop.
3-Check feed back linkage with touch any part of the body.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / imran
First check its feedback link spring if it is ok then
checked its feedback potentiometer by removing it from
positioner with meter.these r main causes that already i
faced.
Is This Answer Correct ? | 0 Yes | 0 No |
what is difference between RTD and Thermocouple?
why we use 3 wire rtd direct wiring for temperature measurement instead of temperature transmitter like bearing temperature
what are procedure of sox-nox calibration
Why went
WHAT IS THE CAM POSITION IN CONTROL VALVE POSITIONER ? WHY IT IS USED?
How a oxygen sensor & analyzer work at boiler or furnace, what’s the principle & science is beyond this, How O2 sensor scene & convert signal & move toward analyzer & analyzer show reading in percent?
1 Answers GS Engineering Construction, KNIC,
What is DeltaV?
What is cascade control in process instrumentation?
4 Answers Engineers India, ITC Infotech,
Can I calibrate the Electromagnetic Flow Meter on line and How.
what is plc?
27 Answers HPCL, KRL, Noor Company, Petrochemicals, SS Automation,
What is Actuator?
difference between span and range