how to convert transmitter milliamps output to like
temp,pressure etc.....
Answers were Sorted based on User's Feedback
Answer / nitin patil
i am giving here the formula for the same,
temp/ pressure = (ma - 4)* span / 16
where, ma = what you measured by multimeter
span = max range of the transmitter.
| Is This Answer Correct ? | 51 Yes | 6 No |
Answer / arun raja.s
Eg. you want to convert in DCS mean it for pressure
transmitter
field pressure Range : 0-100 Bar
Transmitter Calibration Range : 0-100 Bar so output 4-20
mA Depent on the Transmitter input pressure.
This output cable goto Analog input module, in DCS have
to set 0-100 Bar it work depent on 4-20 mA input.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / mastersensor80
the sensor in the transmitter sense the physical effect
(pressure/level/flow) in the transducer this effect is
converted to electrical effect where we can measure 4 -20
ma for example that on the transeducer and the sensor
part,but to answer the above question it is mainly as
answered by Nitin Patil it is merly calculation as the
forumla provided by Nitin.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / neeraj pundir
with the help of transducer we convert (temp,pressure) in
outputs milliamps signals.
| Is This Answer Correct ? | 5 Yes | 3 No |
Milliamps output can be converted to temperature or
pressure, by means of converting the amps to volt by placing
a 250ohm resister across the circuit.
| Is This Answer Correct ? | 11 Yes | 18 No |
if we open the inlet of an air regulator ,how it will affect the out put of regulator? (out put of regulator is using to operate an on-off valve.it is an air to open valve,and valve is in open position.my doubt is air regulator will hold the valve in open or not,if there is no consumption or leak in regulator out put side ,we only loose the input pressure.)
why does a transmitter o/o signal starts from 3-15psi or 4- 20mA?
why is honed type flow orifice plate? what purpose it used? how to select this?
What are the instrumental diagram of valve.
1.Give example of analog and digital signal 2. What is yhe advantage of 8086 than 8085
5 Answers Bhel, College School Exams Tests, Profitec,
3. Differentiate between ultrasonic flowmeter and radar type flow meter.
how to control pid
what is the procedure of belt scale calibration?
WHAT IS D/O D/I AND A/O A/I PLZ EXPLAIN
what is the difference between the microcontroller and PLC?
Instrumentation engineer please reply me,I am electrical engineer ,what is the future in instrumentation dept {presently working (P&ID) Design} for me,whether good future for me as instrumentation department.what side can i get job in future
How process line mpm calculation is done?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)