In the field and in the control room different power
supplies if used How to handle the ground
Normally there should be different grounds in control room.
DCS or PLC vendor generally gives the drawing.
Mostly it is taken as convension that there should be 3
different grounding busbars in control room.
1. One is for the power earth. This will give the earthing
to the power distribution panel of the DCS or PLC.
2. Second is the Signal earth. All the shield cables will be
connected to this earthing busbar to minimize the
interference in the analog signal cables.
3. Thrd is Panel earth. This will be connected to the panel
body.
All these 3 busbars should be connected to 3 different
earthpits by 3 different Copper cables. Redundancy of
earthpits or copper cables may be there if possible.
Is This Answer Correct ? | 3 Yes | 1 No |
Can we measure pressure using differential pressure transmitter? If yes then how?
Tell me the field calibration procedure step by step with diagram of pressure gauge, pressure switch, pressure transmitter, temperature switch, level switch, flow switch, flow transmitter.
What is two wire system and how it work
An equipment is certified for EEX, IA, IIC, T6, what do you under stand by this.
What is shriking and swell effect for a boiler ?
Hi,can anyone help me out with PhD programs related to Instrumentation field?I have a degree in electronic Instrumentation?
What is mean by AC voltage and DC voltage
what is meant by control valve sizing?
in the pipe line if the control valve fails to respond to controller action,by what means we can stop the flow in the pipe line ?
Someone please do mail me some instrumentation questions for Hindustan Petroleum test to avinalexander@gmail.com .Really would be gateful if someone could help me
3 Answers HPCL, Immersion, IOCL,
what is mean by loop checking?
What is actuator what is motorized control valve?