what is the purpose of %impedance for transformer
Answers were Sorted based on User's Feedback
There are two basic purpose of % impedance of transformer.
1. We can check the fault level of the transformer.
2. During the parallel operation of transformer, both transformer % impedance should be identical for load sharing. other wise which transformer has less impedance it will take more load.
its the basic need of parallel operation for two transformer.
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / guest
%impedance is to know the short circuit current of
transformer,depend on transformer ratings , for ex: 1600kva
6%,20 mva 10%
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / suseendran
It is the output voltage drop when transformer is fully
loaded..... This can be measured by conducting short circuit
test.....
Is This Answer Correct ? | 0 Yes | 2 No |
how do we calculate contactor and fuse rating for a motor if its full load current is known,i want exact calculation for 1.5 kw motor????
1 Answers Allied Group, Nucon,
why we cannot protect 100% winding of an alternator by using differential protection?
what is function of centrifugal switch in single phase induction motor..?
why motor run slow speed in star connection?explain how?
What are the basic component of a cro?
LT, CC and LMU installed at both the outgoing circuits of 132 kv double ckt transmissio what its means ? and what are there use ?
why in a swquence network representation, the negetive sequence generated voltage is taken as zero?
i asked a funny question in Electrical ohms law V=IR in const temp voltage is directly proportional to current Power p=VI cos@ in that formula Voltage is indirectly proportional to current Try to give me the fact what is happening in Electrical.. contact Thanigai_1984@yahoo.co.in
What is the resonant peak?
How to calculate KW saving for power factor correction from 0.92 to 0.98 at 350KW load?
What is difference between VCB and SF6 breaker
What is Meter MF if External CT Ratio is 150/1 , PT Ratio is 132/110 Meter CT Ratio is 200/1 & Meter PT Ratio is 110/1