Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


what is the safe meggar values for motor, transformer HT, LT
and Cables?

Answers were Sorted based on User's Feedback



what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / ssreenu

megger value varies based on voltage of the system. If I
assume it is a 440 Volts system the megger value should be
min. 1 mega ohm.

Is This Answer Correct ?    72 Yes 29 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / brajesh kumar singh

Megger Value (in Meg Ohms) = (system Voltage + 1)/ 1000

Is This Answer Correct ?    29 Yes 6 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / akshay grover

Megger guys say, the value shall be


Megger Value (in Meg Ohms) = (system Voltage + 1)/ 1000

Is This Answer Correct ?    30 Yes 13 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / imran

Magger value must be more than 2 mega ohm minimum..

Is This Answer Correct ?    34 Yes 19 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / keith

If you need it to keep working, such as a sewage or storm
water pump,most reputable companys would trend the readings
beginning with the date the started servicing the motor and
watch for a dramatic decrease in test readings. One has to
be aware of the capacitance effect that water has on the
motor cable of a submersible pump as well as understanding
that it is normal to see a gradual decrease over a several
year period from above 200 megaohms @ 500 VOLT d.c. ( brand
new)to eventually down to 10 to 20 mega ohms. I have found
that although motors will run down to 2 mega ohms 230 volt
3 phase and 1 mega ohm to .6 mega ohms 480 3 phase they
don't run much longer. More important is to recognize
dratic decreases between monthly to quarterly readings as
they indicate potential failure ( direct short to ground)
which could trip main distribution breakers, thereby
effecting other motors or equipment by robbing them of
power. i.e. Alarm cicuits that are not battery back up
equipped.

Is This Answer Correct ?    7 Yes 0 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / mohammad nazeer

system voltage in kv plus 1kv. if a motor system voltage is
480-v, its megger value should be 1.48megga ohm.

Is This Answer Correct ?    7 Yes 3 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / dhamodaran.j

R>= (rated motor voltage/1000 +1)*10 (M ohm)

Is This Answer Correct ?    3 Yes 0 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / v. srinivasa rao

It is depending on megger voltage if it is 1000 v megger the
equipment must be 100 M Ohm minimum value it is 5000 v ht
megger it must be 10 G Ohm minimum value.

Is This Answer Correct ?    4 Yes 2 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / gins

More than 50mega ohms say that reference saramco check list
for megger test and for a hipot test this range will be more
than 100micro ampere.

Is This Answer Correct ?    10 Yes 9 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / khan

there are some standard meggar values for transformers lt/ht
motors cable.

Is This Answer Correct ?    3 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

why ie corona losses in tranmission line

1 Answers  


why firewall is build up between two transformer (220/11kv,50MVA)?what should be the firewall height?what is the clearance between firewall and transformer?

2 Answers   Siemens, Tous Stadt,


why we avoid parallel operation of diesl generator?

4 Answers  


how we can save electrical energy in industries,please give some inputs

3 Answers  


Why Utility Distribution System in India is mainly at 11 kV? Why not Utility go for 33 kV?

0 Answers  


what is let through energy of mccb

2 Answers  


can we choose current transformer secondary, to calculate residual flux in a power transformer, so as its saturation is close to the saturation level of power transformer?

0 Answers  


We have isolation transformer 25kvA & ONLINE UPS 15KvA (3PHASE I/P,3PHASE O/P)where isolation should have connect,before UPS or after please brief.

1 Answers   DRJ ARDE,


how to synchronize 4 nos. of diesel generator sets of different capacity (kva)?

7 Answers   Bhel,


how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?

0 Answers  


How to determine alternating current frequency?

0 Answers  


whether starting current is limited to rated current of motor through soft starting or it exceeds the rated current?

0 Answers   DAE,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)