Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


what is the safe meggar values for motor, transformer HT, LT
and Cables?

Answers were Sorted based on User's Feedback



what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / ssreenu

megger value varies based on voltage of the system. If I
assume it is a 440 Volts system the megger value should be
min. 1 mega ohm.

Is This Answer Correct ?    72 Yes 29 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / brajesh kumar singh

Megger Value (in Meg Ohms) = (system Voltage + 1)/ 1000

Is This Answer Correct ?    29 Yes 6 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / akshay grover

Megger guys say, the value shall be


Megger Value (in Meg Ohms) = (system Voltage + 1)/ 1000

Is This Answer Correct ?    30 Yes 13 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / imran

Magger value must be more than 2 mega ohm minimum..

Is This Answer Correct ?    34 Yes 19 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / keith

If you need it to keep working, such as a sewage or storm
water pump,most reputable companys would trend the readings
beginning with the date the started servicing the motor and
watch for a dramatic decrease in test readings. One has to
be aware of the capacitance effect that water has on the
motor cable of a submersible pump as well as understanding
that it is normal to see a gradual decrease over a several
year period from above 200 megaohms @ 500 VOLT d.c. ( brand
new)to eventually down to 10 to 20 mega ohms. I have found
that although motors will run down to 2 mega ohms 230 volt
3 phase and 1 mega ohm to .6 mega ohms 480 3 phase they
don't run much longer. More important is to recognize
dratic decreases between monthly to quarterly readings as
they indicate potential failure ( direct short to ground)
which could trip main distribution breakers, thereby
effecting other motors or equipment by robbing them of
power. i.e. Alarm cicuits that are not battery back up
equipped.

Is This Answer Correct ?    7 Yes 0 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / mohammad nazeer

system voltage in kv plus 1kv. if a motor system voltage is
480-v, its megger value should be 1.48megga ohm.

Is This Answer Correct ?    7 Yes 3 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / dhamodaran.j

R>= (rated motor voltage/1000 +1)*10 (M ohm)

Is This Answer Correct ?    3 Yes 0 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / v. srinivasa rao

It is depending on megger voltage if it is 1000 v megger the
equipment must be 100 M Ohm minimum value it is 5000 v ht
megger it must be 10 G Ohm minimum value.

Is This Answer Correct ?    4 Yes 2 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / gins

More than 50mega ohms say that reference saramco check list
for megger test and for a hipot test this range will be more
than 100micro ampere.

Is This Answer Correct ?    10 Yes 9 No

what is the safe meggar values for motor, transformer HT, LT and Cables?..

Answer / khan

there are some standard meggar values for transformers lt/ht
motors cable.

Is This Answer Correct ?    3 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

A 25MVA 3300/400V T/F is termed as per winding is …… a) primary 3300V & Secondary 400V b) primary 3300V & low voltage winding 400V c) High voltage winding 3300V & Secondary 400V d) High voltage winding 3300V & low voltage winding 400V

4 Answers   Engineers India Limited,


What is difference between ON delay and OFF Delay Timer?

7 Answers  


hi friends i m from electrical branch and seeking for tech. + apti. both papers of hpcl plz get it available as soon as possible

0 Answers   Engineers India, Engineers India Limited,


what is AB switch???

6 Answers   NTPC, Simplex,


What Is HO factor in power selection

0 Answers   Wonderla Holidays,


what is slip ring startor

1 Answers  


define reflection method?

0 Answers  


whatare the disadvantages occur,if the form factor of transmission will not be equal to 1.11

0 Answers  


Name different types of fault and which instrument is used to measures earth,short,open cicuit fault?

6 Answers   NTPC, Vijai Electricals,


how the frequency was generated in power station

2 Answers  


An AC coil to give DC supply whats happen in the coil.what type of problem are create.

2 Answers  


Is there any calculation to find unknwon(unferroled) phases R Y B in alternator,3 phase motor anybody shoot my problem. how can we notice this is the respective phase?

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)