Answer / hareesh k soman
There r two reasons for the star and delta connection.. one
is load requirement i.e if load is un balanced we will go
for star.. i.e neutral will ground the fault current where
the delta will use for balanced load.
other reason is insulation requirement .. i.e in Power
transformer HV side will be star connected and LV side will
be delta connected. for example in 220kV/132kV power
transformer, in star connected HV line to line voltage is
220kV and phase voltage is 127kV i.e its required lesser
insulation. but in delta connected system V line= V phase
i.e 220kV insulation is required. but star only 127kV is
required...
| Is This Answer Correct ? | 41 Yes | 6 No |
Answer / tiang cs
HV system is mainly in connected in star connection because
of high insulation cost is needed for the HV system. If HV
connected in delta connection, and 1 phase shorted to
ground, then the phase voltage will become line voltage
which threathen the isulation in HV system.
Medium voltage usually connected in Delta connection
because no neutral is needed and if 1 phase shorted to
ground, the medium voltage system is unaffected and remain
operational.
For low voltage side, the connection is usually star
connection cause the neutral is needed for single phase
power supply. Besides that, LV system is most commonly
access by human and for safety reason, star connection is
prefered.
| Is This Answer Correct ? | 9 Yes | 4 No |
Answer / kidus mizan@yahoo.com
if the amount of power to be transformed is greater than that w/c can be handled by one transformer, it become necessary to employ two or more unit in parallel.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shahbaz shaikh
as we use the transformers for the step up or step down the
electrical quantity and when we use star/delta there is some
relation between line and phase quantity which help in the
connections
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / pavan kumar
the reason behind is to eliminate the triplen harmonics
| Is This Answer Correct ? | 6 Yes | 15 No |
Answer / rashid
As per question, we use delta /star or star /delta as per
our system requirment bcoz we need star connection to get a
nuetral and phase for our protections in case of delta we
are not able to do this, and otherwise the delta connection
is better for system stability also we also need star at
end users where we need single phase supply,
| Is This Answer Correct ? | 6 Yes | 20 No |
Answer / s p
Transformers are in such a way bcos they are either step up or step down. In case of Step down the configuration is Star to delta & the other way if it is Step up. It is to protect the transformer & the equipments safety.
| Is This Answer Correct ? | 5 Yes | 29 No |
Main purpose of using transformer is to convert the power,
Either from high to low or vice versa....i e step up or
Step down....for more deatils go through Power plant or
power system books.. Why transformer is neccessary in
transmission net work..n How the power will converted from
high voltage to low voltage..etc
| Is This Answer Correct ? | 5 Yes | 35 No |
how will we calculate the copper wire load..
In EHV tranm. The conductors are …….. a) Cu roads b) Cu bars with Si c) Cu tube with Si plate
2 Answers Engineers India Limited,
What is the difference between lubricating oil and insulating Oil?
what are the difference between protection class CT and Class PS CT
how to identify the failer of igbt
what is meant by cbct elr?
1.how to calculate energy units in our home at singe phase, 2.415V,63A wiring what will use thickness of wire
A shopkeeper allows 10% discount on the price of an article and sells it for Rs 7,600. What is the marked price of the article?
how to calculate a cable size while load is given in amp or kw and length is also define.?
a transformer can beb used as aload?give discription
2 Answers Esses Eltech Systems,
can i connect REF and Differencial relay in 1 CT core for transformer protection?
can you show me the components inside a air circuit breaker with connection diagram?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)