Answer / hareesh k soman
There r two reasons for the star and delta connection.. one
is load requirement i.e if load is un balanced we will go
for star.. i.e neutral will ground the fault current where
the delta will use for balanced load.
other reason is insulation requirement .. i.e in Power
transformer HV side will be star connected and LV side will
be delta connected. for example in 220kV/132kV power
transformer, in star connected HV line to line voltage is
220kV and phase voltage is 127kV i.e its required lesser
insulation. but in delta connected system V line= V phase
i.e 220kV insulation is required. but star only 127kV is
required...
| Is This Answer Correct ? | 41 Yes | 6 No |
Answer / tiang cs
HV system is mainly in connected in star connection because
of high insulation cost is needed for the HV system. If HV
connected in delta connection, and 1 phase shorted to
ground, then the phase voltage will become line voltage
which threathen the isulation in HV system.
Medium voltage usually connected in Delta connection
because no neutral is needed and if 1 phase shorted to
ground, the medium voltage system is unaffected and remain
operational.
For low voltage side, the connection is usually star
connection cause the neutral is needed for single phase
power supply. Besides that, LV system is most commonly
access by human and for safety reason, star connection is
prefered.
| Is This Answer Correct ? | 9 Yes | 4 No |
Answer / kidus mizan@yahoo.com
if the amount of power to be transformed is greater than that w/c can be handled by one transformer, it become necessary to employ two or more unit in parallel.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shahbaz shaikh
as we use the transformers for the step up or step down the
electrical quantity and when we use star/delta there is some
relation between line and phase quantity which help in the
connections
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / pavan kumar
the reason behind is to eliminate the triplen harmonics
| Is This Answer Correct ? | 6 Yes | 15 No |
Answer / rashid
As per question, we use delta /star or star /delta as per
our system requirment bcoz we need star connection to get a
nuetral and phase for our protections in case of delta we
are not able to do this, and otherwise the delta connection
is better for system stability also we also need star at
end users where we need single phase supply,
| Is This Answer Correct ? | 6 Yes | 20 No |
Answer / s p
Transformers are in such a way bcos they are either step up or step down. In case of Step down the configuration is Star to delta & the other way if it is Step up. It is to protect the transformer & the equipments safety.
| Is This Answer Correct ? | 5 Yes | 29 No |
Main purpose of using transformer is to convert the power,
Either from high to low or vice versa....i e step up or
Step down....for more deatils go through Power plant or
power system books.. Why transformer is neccessary in
transmission net work..n How the power will converted from
high voltage to low voltage..etc
| Is This Answer Correct ? | 5 Yes | 35 No |
gd eve frndz my qstn is how convert sound energy to electrical energy
if the stetor speed (N S) increase by 20% then the rotor speed will be increased by 20% is it true. ?
415v 14kw so can u tell me how i can measure the cable size.then size of the earth also
What is master trip relay? How does it work?
how to calculate single phase motor efficiency ?
what does mean of RCT and STR in diffrential CT?
In Power Line Communication (PLC) the wave trap is used to block communication signals from entering neighboring lines. My question is this: Why do they allow for different filtering arrangements on these wave traps? Isn't it always going to be a low pass filter since we want the power frequency to go through, and the comm signal blocked?
What is a Phase shift meter? Where can I get one?
Why alternators are designed at 0.8 pf lag?
What is Grounding?
which cable is used for 15 Hp monoblock pump 3phase and service wire Distance is 210 feet please tell me cable size Armaured
Why the stator is rotated in ceiling fans not Rator?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)