if power factor comes in leading & showing -0.95. Is there
any effect on electrical system? if yes, then please tell me
what would be the effects. & how long we keep power factor
in leading.
Keeping power factor in leading shows more KW & less KVA is
it correct or not.
Answers were Sorted based on User's Feedback
Answer / santosh kawade
It is not recommended to keep power factor leading:
1) We try to keep power factor unit to reduce transmission
losses, this main purpose will not achieved by keeping
leading power factor. If power factor is lower than unit
(it can be leading or lagging) transmission loss will
increase.
2) During leading power factor if we make any breaker
operation (close/open)it will generate high voltage across
breaker, which is harmful to breaker. For capacitive load
operation we need a special breaker.
3) It is not correct that keeping leading power factor
shows more KW and less KVA.
Santosh Kawade
9224 69 3116
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rahamadulla.m
Yes there is effect on electrical system.The power will be
lost and could not maintain the voltage in the capacitor
bank system. so we can keeping power factor in leading
shows more KW and less KVA.It is correct.
| Is This Answer Correct ? | 2 Yes | 2 No |
What is the material used for the core of a high freiquency transformer?
how to do the ductor test?
WHY THE COLOR OF OUTDOOR TRANSFORMER IS BLUE ONLY???
How to calculate Ith (I thermal) for curent transformer
Tell me about ur past electrical maintanence job
0 Answers Apollo Power, Solar,
what is let through energy of mccb
In a house wiring why we are using only one neutral wire and so many phase wires from the main board, when the load is common for both wires?
the minimum clearance b/w ceiling and plane of leaf of ceilng fan shall be ..........mm
what is the difference between isolation and insolation ? please explain in detail with example.
what is stper motor.what is its uses
A 25MVA 3300/400V T/F is termed as per winding is …… a) primary 3300V & Secondary 400V b) primary 3300V & low voltage winding 400V c) High voltage winding 3300V & Secondary 400V d) High voltage winding 3300V & low voltage winding 400V
4 Answers Engineers India Limited,
7- What is the Dissipation Factor and the difference between it and Insulation Resistance Test? 8- What is the task (function) of DC and AC reactors in power plant? 9- What is the task (function) of (open delta with earthed) in some types in transformers? 10- What is the base of the selection of the vector group in transformers? 11- What is the zig-zag transformer and its function by drawing in large detail? 12- What is the polarity ? 13- Why we make short between phase(R) in high side and phase (r) in low side in vector group test? Where High Side ( R ,S and T ) and Low Side ( r ,s and t ). 14- What are the time on delay and time off delay? 15- What is the vector group? 15- What is the task (function) of different types of vector group such as Dyn11 , Dd0 , YNd1,……..,?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)