if power factor comes in leading & showing -0.95. Is there
any effect on electrical system? if yes, then please tell me
what would be the effects. & how long we keep power factor
in leading.
Keeping power factor in leading shows more KW & less KVA is
it correct or not.
Answers were Sorted based on User's Feedback
Answer / santosh kawade
It is not recommended to keep power factor leading:
1) We try to keep power factor unit to reduce transmission
losses, this main purpose will not achieved by keeping
leading power factor. If power factor is lower than unit
(it can be leading or lagging) transmission loss will
increase.
2) During leading power factor if we make any breaker
operation (close/open)it will generate high voltage across
breaker, which is harmful to breaker. For capacitive load
operation we need a special breaker.
3) It is not correct that keeping leading power factor
shows more KW and less KVA.
Santosh Kawade
9224 69 3116
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rahamadulla.m
Yes there is effect on electrical system.The power will be
lost and could not maintain the voltage in the capacitor
bank system. so we can keeping power factor in leading
shows more KW and less KVA.It is correct.
| Is This Answer Correct ? | 2 Yes | 2 No |
why current increases when voltage decreases in ac system
what is ballast
CAN WE CALCULATE THE NEGATIVE SEQUENCE AND ZERO SEQUENCE REACTANCE OF A GENERATOR USING ONLY ITS RATED VOLTAGE, KW, PF AND SYNCHRONOUS REACTANCE??? IF YES, THEN HOW??
What are difference between earthing switch and earthing truck ? What is the operation philoshopy of earthing truck ? Wht are the component of earthing truck ?
Why we should not parallel the with EB
1)Explain why the cradle guard is used on railway crossing in overhead line construction?
What is the difference between MCCB and MCB ?
HELLO EVERYONE, I RECENTLY HAVE FOUND ONE PROBLEM, I WAS TAKING NO LOAD TRIAL OF AN HT MOTOR 920 MOTOR , 1440 RPM , 6.6 KV, WITH AUTO TRANSFORMER. AT 450 V, LOAD WAS 40 AMP AND SPEED WAS 250 RPM. BUT AS WE INCREASE VOLTAGE FROM 450 TO 480V, LOAD BECOME 41 AND SPEED REDUCED TO SOME RPM . SO WHICH PHENOMENON ACTED HERE FOR REDUCING SPEED.?? AND IS IT HAPPENING ALWAYS OR IT IS RARE? I ALSO HAVE FACED SUCH PROBLEM WITH FEW LT MOTOR ALSO.
What is drain current of static relay?
explain transformer ct connection?
Can we indroduce the principle of single phase induction mator to Transformer? i.e. by Producing rotating flux in the transformer.
why industry prefer ht motor instead of lt motor.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)