if power factor comes in leading & showing -0.95. Is there
any effect on electrical system? if yes, then please tell me
what would be the effects. & how long we keep power factor
in leading.
Keeping power factor in leading shows more KW & less KVA is
it correct or not.
Answers were Sorted based on User's Feedback
Answer / santosh kawade
It is not recommended to keep power factor leading:
1) We try to keep power factor unit to reduce transmission
losses, this main purpose will not achieved by keeping
leading power factor. If power factor is lower than unit
(it can be leading or lagging) transmission loss will
increase.
2) During leading power factor if we make any breaker
operation (close/open)it will generate high voltage across
breaker, which is harmful to breaker. For capacitive load
operation we need a special breaker.
3) It is not correct that keeping leading power factor
shows more KW and less KVA.
Santosh Kawade
9224 69 3116
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rahamadulla.m
Yes there is effect on electrical system.The power will be
lost and could not maintain the voltage in the capacitor
bank system. so we can keeping power factor in leading
shows more KW and less KVA.It is correct.
Is This Answer Correct ? | 2 Yes | 2 No |
what will happen when excitation of a synchronous machine is suddenly reduce to zero when it is running at full load..??
What are the methods/types of distance protection schemes used in transmission system?
What is the difference between UPS and SMPS?
can u give me a brief idea about power line carrier communication ??
how much cable size required for 70 kilowatt load.
1.what is bus cuplour and main funtions. 2.what is main function of alternator. 3.how many types of dg oils.
Why the generator rating in kva
32 Answers CompuCom, DLF, Genpact, HNG, SIPM,
why 15 kw motor winding resistance is low then 5 kw motor winding resistance?
are there rmu for 3 transformer?
1000kva = how much kvar
In single phase capacitor motor, if the motor rotate reverse direction then how much power will be consumed by the motor and why?
why we use post insulators in no ofstacks at substation for supporting equipment ? why we not use single post insulator