what is the procedure for three phase motor differential
relay testing
can it do with single phase test kit?
Answer Posted / santosh kawade
Three phase motor differential relay testing can be done
with single phase test kit.
There are two type of relay testings:
1) Primary injection : In this testing entire system
(including relay, control wiring and power wiring get
checked),
2) Secondary injection : In this testing generally we check
relay only.
By using single phase test kit:
1) Primary injection :
a) Carryout shorting of all three phases of motor winding
by using short link for individual phases seperately.
b) Inject current by using current injection device (for
inzone and outzone fault)
3) Check stability of relay for outzone fault and operation
of relay for inzone fault.
2) Secondary injection :
Directly inject fault current in relay terminal and check
proper operation of relay.
Santosh Kawade
9224 69 3116
| Is This Answer Correct ? | 6 Yes | 2 No |
Post New Answer View All Answers
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
how to calculate energy of 3-phase motor?
what happen if generator of micro hydro running at only a small percentage of its capacity, as a comparison, if the diesel generator that runs on only a fraction of its capacity there will be a wet stacking
How can find thermal state value in relay for calculate thermal overload.
I want to put this query to SENIOR & EXPERIENCED ELECTRICAL ENGINEERS. 1)I want to know about the control circuit diagrams for control panels. I found it difficult to understand. Is there ant booklet through which we can learn the circuit diagrams? 2)I want to learn about conduiting, laying cables, preparing cable schedules and various techniques which is the part of building infrastucture(construction field). I don't have any experience in this area. I have experience in control panels only. that's why i am not getting any opening in building infrastucture (construction field).Can I get the job in this field as Trainee Engineer? How to enter this field? I need job in PUNE
v/f drive basic princeple
what is cathodic protection and why it use in industries?
why power factor is important?
ELECTRICAL ENGINEER TEST IN FEWA ANY ONE HAVE KNOWLEDGE ABOUT THIS?????????
What are n circles?
Define early construction of human being
What is the difference between Droop vs Isoch Control?
i need to now what will be the cable size to the following load, transformer to distribution panel distance 110m, load 1000kw, voltage 400v, pf 0.85, permissible voltage drop 2.0%, overhead line, atmospheric temperature 35 degree c.
How phase to phase voltage comes 440V.
what is the relation between knowing of the distance between power transformer and the capacitor feeder in case of parallel operation