3 ph motor connected in star delta starter. when we start
the motor it run in star but when in is going in delta it
trips the main incoming supply. why?
Answers were Sorted based on User's Feedback
Answer / deepak r thakur
simple when motor start in star three phase going to
winding correctly but when its going in delta motor two
winding connect with 440votl but 3rd winding connect same
phase so motor going in singal phasing & its get heavy
currunt it trips the main incoming supply.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / rajesh kumar sharma
Two conterctor hold on star running time after some time a conteractor whose shrt three terminals has unhold and delta conteractor is hold it change only one sccond time.
if the timer switch is not working than creat a problam.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / anurag tiwari
Dear friend,
there are three point u have to check
1)first u check the motor winding.
2)check the timer and set the delta time.(appox 6sec).
3)If u are using mpd relay .May be your CBCT is saturated.
Is This Answer Correct ? | 0 Yes | 0 No |
what is the switching substation
What are the types of TESTS in CIRCUIT BREAKERS based on Testing and commissioning?
What are the Formula of computing Back up Time of 500kVA UPS with 4 Battery Banks, each bank composed of 43 pcs of Batteries 12V150Ah. How to compute the Back up Time of UPS? We have also 3X500kVA UPS running in Parallel same composition as I write above.
coil is consist of
why is using sensor?what is differece between photoelectric and proxmitty?
when we r using 3.5 cable for a bldg. and put laod on each phase using the neutral and neutral is the return paht for the phase so the current of the neutral must be Ir+Ib+iY (return).But the size of the netural is .5 as comper to the phase.
How calculate the Transformer Impedence With Example
What are the site acceptance tests for power cables, DG Sets, LT panels & 30kVA UPS ?
why we ht line cable size small rather than lt cable.
what type of transformer used in soft ware parks its distribution or power transformer. like 1800 kva
During he starting up of the motor, the upstream's MCCB (350A) always trips due to the UVT relay activated. Can Star-delta starter use for a 20kW Motor (For a powder mixer machine) cause voltage-dip in the supply line voltage? If so, what are the recommended solution to eliminate/reduce the transient voltage dip in the line voltage?
What are dependent sources?