we want install 11KV generator to supply power 12km far
from the power house.Load to be fed is 1MW.which conductor
should we use and wat will be transmission line losses?
Answer / k.prakashchandra
The current is 52.5 A at unity pf, add 20 % .It is about 60
A. You can use Rabbit conductor
| Is This Answer Correct ? | 0 Yes | 1 No |
WHAT IS MEANT BY SHEATH VOLTAGE IN 132Kv cable?
why transformer rating in kva?
What is mean by nominal voltage,Explain?.How much nominal voltage?.
can any one tell in easy method for circulating current ??
how do you choose the cable size as per amps rating & the voltage drop for the same.
Why substation battery room is coulered black?
How to calculate the Meter constant for the given Meter (by using any formula)
i am gng to visa interview this july i have 4 backlogs gre 1010,toefl 75,pls give me the tips pls pls
is that a problem if i connect a single phase load to a secondry delta connected transformer but i get a neutral from other transformer i the system?
What would be the ratio of a Delta-Wye tranformer having 48000 volts phase to phase on the primary and 4160 volts phase to phase on the secondary?
why there is 1 phase and 3 phase but not 2 phase and 4 phase?
hi how are you? i m in walchand college of engg. do you have interest in join me through email so send your email id
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)