1. How many output signals do wew have in process control?
2. Could you write down the names of the pre-commissioning
and commissioning stage test instruments and explain them
(more than 5 items)?
3. What is the first step to commission a transmitter on
service?
4. What is RTD?
5. Find the output value in MA of a temperature transmitter
(RTD Type) at 120degree celius?
6. What is the O/P signal of a pneumatic transmitter?
7. What is the O/P signal of an elctronic transmitter?
8. What is the close loop and open loon?
Answers were Sorted based on User's Feedback
1. Two output signals are used in process control -
analogue and digital.
2. RTD - Resistance Temperature Detector for temperature
measurement upto 600°C.
3. O/P signal for pneumatic transmitter is pneumatic signal
3 - 15 psi
4. O/P signal for electronic transmitter is electrical
signal 4 - 20 mA, 1 - 5 volt.
5. Close loop having sensor, transmitter, controller, and
controlling element (like control valve, on off valve,
damper, servo motor). Open loop does not have controlling
element. open loop is used for only indication in control
system.
Is This Answer Correct ? | 21 Yes | 0 No |
Answer / biswarup das
Answer of Ques No.5)) Transmitter(Tx) o/p depends on
calibration range. If the Tx is calibrated in the range
0-120degC. Then it will show 20ma when the actual
temperature would be 120degC.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / kalla anil kumar,jeypore
1- it may analog and digital, or
2- lot of test instruments like pressure calibrator dead weght testor,(DRUCK),temperator calibrator DECODE BOX,temp bath,For control valve mA source,for vabration (vabolator) etc.
3- we have know the tag,location and application of transmitter,
4-RTD- Resistance temperature detector, it is used up -200 to 600 deg C,
5- first we should know transmitter Range, then we calculate mA, if the range is 120 then 0deg 4mA,30deg 8mA,60deg 12mA,90deg 16mA and 120Deg 20mA,
6- .2 to 1 kg/cm2 or 3 to 15psi
7- 0 to 20mA, 4 to 20mA
8- in a close loop PID control,transmitter, and final control element like control valve,on/off valve, and MOV etc, it will work on auto there will be set valve then controlling out put will come from PID-C, in open loop there will be no set point we have control by manual,
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / p.sharathreddy
4. o/p signal of electronic transmitter is 4-20 mA and 1-10 mV
dc
Is This Answer Correct ? | 1 Yes | 8 No |
What is rtd output signal
Rtd sensor how to calibrate
how to calibrate control valves & power cylinders & ultra sonic level transmitters
Tell me the field calibration procedure step by step with diagram of pressure gauge, pressure switch, pressure transmitter, temperature switch, level switch, flow switch, flow transmitter.
hello friends, can you please send me the model paper or question paper to be prepared for hpcl examinations????????? You can mail me at rahim_here@yahoo.com waiting for your reply........... help me .. plz.....
in which mode of the zener diode act when load voltage is approximately constant
How flow control valve is working with pnuematic positioner and I/P convreter from command is given from remote
What is the difference between sdv and bdv ?
I am a electronics and instrumentation fresher trying for a job in IT sector. what do need to prepare for the interview?
how to given power supply of any type two wire transmitter in field?
how can i calibrate the temperatuture gauge used by temperature bath(dry block) i mean step by step procedure?
How to calibrate vertex flow meter? How to calibrate mass flow meter?