When should I use earth leakage circuit breaker for incomer
and when should I use it for each feeder seperately?
Answer / mubeen
If your load is unbalance,or distrubting to different
panels you should use Earth leakage relay not ELCB.ELCB can
be used for branch circuit or any sperate panel such as for
light, power sockets etc.Earth leakage relay can be use to
trip the breaker on calculated current.
| Is This Answer Correct ? | 1 Yes | 0 No |
what is method for testing CT
What is the difference between Ac curent & DC current
what is V.L.F. testing of power cable? do you know the voltage ratings, like for what rating and size of cable what rating of V.L.F. testing is used?
what is closing resistor in circuit breaker? why it used?
How the size of transformer decreases if we increases the frequency?
one KVAR takes how much amps, and how to add power capacitors to electrical panels, for example if one of the MCC drawn 800amps means how much KVAR required
What is Instantaneous Earth fault relay,how will work
What are your personal skills and abilities for such a Master Course and your possible preparation to undertake this course?
Why the high starting current does not harm the low capacity induction motor?
Why a single-phase induction motor not an inherently self-starting machine?
11 Answers ETC, Hindustan Shipyard,
why we use perllel conection system in the wiring?
why capacitor bank is not used in generator power
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)