What are the different pre-commissioning tests that are
performed on the distribution transformer, power cable and
switchgear (11kv)?
Answer / pillay
Most importantly the insulation and HV holding test is done on
all the installations.
on the tx former;winding insulation test,
ratio test, vector group test,impedence test, oil dielectric and
other test,
bucholtz relay test, all protective equipments operation test,the
switchgears insulation and conductivity tests along with pressure
tests on cables also . all tests have to meet the local
requirements or as relevant BS.
| Is This Answer Correct ? | 15 Yes | 3 No |
Why can't we parallel Voltage transformer secondary circuits?
what is the full load current and power rating of 1 Tonne Air Conditioner?How will Calculate?
in slip ring motor if motor specification is given how we calculate its rotor resistance in starting
The coulomb is a unit of:(a) Energy(b) Voltage(c) Power(d) Quantity of electricity
how to calculate circuit breaker capacity
How to calculat size of copper & aluminium ?
why the current is denoted by the letter 'i'
why HT motors are earthed only at equipment side & for it's single core cable with aluminium wire armoure using?
1 Answers Legrand, NLC Neyveli Lignite Corporation Limited,
If any cable burnt how can we identify it burnt by high current of high voltage?
1.What is isolators and bus bars?give answer in details
What happens when the power factor is leading and its disadvantages.
how synchronous generator can be used as synchronous condenser?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)