explain in detail HV & LV bushing connection in power
transformer (110 / 11 kv 16 MVA)
Answers were Sorted based on User's Feedback
Answer / sudhirkumar singh
THE HV BUSHING i.e 110KV SHOULD HAVE THE CAPACITY TO WITH
STAND THE RATED KV i.e 110KV,AND IF IT IS HAVING THE WITH
STAND CAPACITY MORE THEN THE RATED KV THEN IT CAN BE
CONNECTED TO HV OF THE POWER T/F.IN SAME WAY THE LV BUSHING
SHOULD HAVE THE CAPACITY TO WITH STAND THE LV RATED VOLTAGE
i.e 11KV,THEN ONLY IT CAN BE CONNECTED TO THE LV OF THE
POWER T/F i.e OF 16MVA.
| Is This Answer Correct ? | 12 Yes | 4 No |
Answer / satish
here in 111/11 kv 16 MVA)transformer the hv side is 110kv
side i.e primary one whereas secondary side is 11kv is lv
side.
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / talluri
Bushing connections at HV side is 3 and LV side is 4 with
highly insulated.Normally at substations 110/33 transformer
will be used and then same 33kv will be step down to 11kv
to avoid losses.
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / satheesh k
HV side bushing connection is only 3 terminals R,Y, B. In
LV side 4 terminals are there R, Y, B, N. Neutral is
grounded in station transformers. But in distribution
transformers the neutral is not grounded in secondary and
is extended to commercial use.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / shyamkr
here in 111/11 kv 16 MVA)transformer the hv side is 110kv
side i.e primary one whereas secondary side is 11kv is lv side.
| Is This Answer Correct ? | 8 Yes | 12 No |
what is sinwave ups
How many current ratings of MCB's are in the market? e.g: 1A, 2A, .......upto.
Why does inductive loads consume KVARs?
What is the acceptable resistance range of UPS battery
Connection diagram for KW meter and Kva meter
if we apply 1000ADC instead of 100ADC or We apply 50ADC instead of 100ADC,What will be happened in the test result value.Pl explain
WHAT IS SYNCHRONISING?
Is it legal of using 3 phase motors in 2 phase in Tamilnadu?
voltage at generation stage is usually- ? a.11kv b.33kv c.66kv d.220kv
for a machine R=130 KVA Y=132 KVA B=144 KVA Then what will be the total kva
Distribution Transformer are connected in configuration? a. Star/delta b. delta/star c. star/star d. delta/delta
what is wave traps and why it is been used in switchyards?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)