how can u determine size of the conductor by knowing the
voltage level
Answers were Sorted based on User's Feedback
Yes one could determine the size of the conductor by knowing
the voltage levels and some other factors too.Also the
maximum voltage that can safely be applied to any winding is
determined by the type and thickness of the insulation used.
When a better (and thicker) insulation is used between the
windings, a higher maximum voltage can be applied to the
windings.
To be more specific by equations,
VD= 2*K*I*L/ CSA
WHERE:
VD= VOLTAGE DROP
I= CURRENT
L= DISTANCE OF THE LOAD FROM THE OUTLET (IN FT)
K= 12 FOR COPPER AND 19 ALUMINUM (FOR MAXIMUM TEMP OF 75 DC)
CSA= CONDUCTOR CROSS SECTIONAL AREA IN CIRCULAR MILS.
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / duminy
you cannot detrermine the size of the conductor by only
knowing the voltage level. awire of just 1mm thickness can
carry 1kv level of voltage. until and unless u complete the
circuit the current wont flow and thus no issues.the
current is the 1 who heats up the conductor n burns
it...dats why we always luk for current carrying cabability
of any conductor not voltage level.
Is This Answer Correct ? | 1 Yes | 2 No |
What are the different parts of Alternator and how it works?
How to conduct a Hipot test on a 11KV cable?
Will u plz give me simple diagram for tube light connection & also function of chock?
8 Answers Bhushan Power Steel, Dalmia Group, Jindal, Practical Viva Questions, TCS, Windmoller,
What is the formula to find out two phase active & reactive power
why we are not giving the zone 1 trip command to the master trip relay
How to select, design,size & calculate for 11 KV/33KV/66KV/132KV/220 KV/440 KV circuit breaker for HT side of transformer protection/HT distribution protection?
What are the typical values of characteristic impedences of overhead line and underground cabel? Why there is so much variation?
how to give earthing in plain?
what is the permissible bend in the LT& HT CABLES.
what is the use of cable in our environment ?
How to checking sld drawingas and control drawings
why transformer not used to starter