how can u determine size of the conductor by knowing the
voltage level
Answer Posted / naveen
Yes one could determine the size of the conductor by knowing
the voltage levels and some other factors too.Also the
maximum voltage that can safely be applied to any winding is
determined by the type and thickness of the insulation used.
When a better (and thicker) insulation is used between the
windings, a higher maximum voltage can be applied to the
windings.
To be more specific by equations,
VD= 2*K*I*L/ CSA
WHERE:
VD= VOLTAGE DROP
I= CURRENT
L= DISTANCE OF THE LOAD FROM THE OUTLET (IN FT)
K= 12 FOR COPPER AND 19 ALUMINUM (FOR MAXIMUM TEMP OF 75 DC)
CSA= CONDUCTOR CROSS SECTIONAL AREA IN CIRCULAR MILS.
| Is This Answer Correct ? | 3 Yes | 3 No |
Post New Answer View All Answers
Which thing is maximum in RLC circuit at resonance a)power consumption b)inductive current c)capacitive voltage
Why lose 1 phase voltage in 33kv to 415v stepdown transformer
how much cable size required for 70 kilowatt load.
Can we use both Electrical & mechanical interlock between tow breakers? if yes how, please explain
When will you multiply and devide with derating factors to the actual value while sizing the cable?
I am applying for NTPC examination.Can we please provide previous paper to my mail prasad.chintala108340@gmail.com
What is core CT & it's function?
1.what is mean by 8/20 micro sec waveshape
WHAT CAUSED THRESHOLD VOLTAGE TO EXIST?
Does outdoor isolator loose connection cause short circuit current in that circuit? if yes then how ??
why do we lay up the core of a cable?
What is Load sharing of Transformer ?
How to calulate Locked rotor amper(LRA) for compressor type motors?
Define Electrical Insulation and examples of Solid,Liquid and Gaseous insulating materials?
3ph motor running with unequal kw and different pf what are the reasons