For 300 MW plant what is the distribution voltage
Answers were Sorted based on User's Feedback
Answer / virendra joshi
It depends that receiving station is how far & also how
many feeders are to be taken. if power is 300 MW then HV
transmission is ideal because the conductor size would be
less & hence the cost of transmission is less. if i would
be the designer i use 400 KV 2 nos feeder to receiving
station.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / joel
The distribution voltage is the LV that you will get. Like
for example in a 300MW 138kV/13.8kV substation, 13.8kV line
will go to the building RMU then this will be step down to
380V for distribution by a distribution transformer
installed in the building.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / jagannath swami
Its fully depend upon the switch yard (EB ) how much distance from ur end as per ER 300 MW power gen. upto 220kv S.S. is required . and the distribution is ur hand
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / khader shah
Distribution voltage will be 380 to 460 volts only for a 300
MW plant
Is This Answer Correct ? | 0 Yes | 1 No |
we have 3 phase 4 wire supply 230/415 V.AC and our distribution is single phase or we have all single phase 220 v,ac operated appliances. and noted the current with help of clamp meter Red to N = 20 Amps. Yellow to N = 45Amps and Blue to N = 30 Amps ( total is 95 Amps ) what will be neutral current on the main .
How to dimensioning SDCCH, LAPD and CS7 signaling on GSM?
can we transmit power with out cable if it is possible how it is possible.
how encoder works?
What is the percentage loss for aluminium wire for HT line more than 11KVa
What is Fire Panel ? How it works ?
Can we indroduce the principle of single phase induction mator to Transformer? i.e. by Producing rotating flux in the transformer.
Iwould like to know barc interview questions
how much leakage current is allowed in MC61A L&T make relay?
what shall be no load voltage of 132/33 kV transformer ? is it 33 kv of 34.5 kV
How one can check the charger of the mobile phone or any other charger .......... that is it working ? if , working is it delivering the required supply which is needed by the battery to charge properly ?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?