How much current will a 5 HP delta connected motor at no
load will take?Is tat need a starter
Answers were Sorted based on User's Feedback
Answer / asif.k64@hotmail.com
1HP=746watt
5HP= 3730watt
power = 1.732*v*I*cos@ for three phase motors.
I=3730/1.732*415*.8
I=6.5A
Hence the motor will draw a no load current approximately
about 6.5 A.
There is a need of a starter.
Is This Answer Correct ? | 13 Yes | 3 No |
Answer / srdhar
please send ap transco accept diploma only ap or all ugc universiti diploma secrtificates
Is This Answer Correct ? | 0 Yes | 3 No |
I NEED RRB SYLABUS FOR JE ELECTRICAL ,PLEASE SEND TO MY E- MAIL ID joo28_eee@yahoo.co.in
What is meant by operating sequence of VCB : 0–0.3sec.–CO– 3min.-CO
what do you mean by PF correction. A motor is rated at 15 kw,415 volts, 0.7 pf and eff of 0.92. The powerfactor is improved to 0.98 by adding capacitors at the bus. calculate the current drawn by motor under full load condition before and after pf correction
Why do we need a separate control desk & PLC control panel in Boiler plant or coal handling plant? Can we provide cost effective Control desk cum PLC panel. Is there is an specific need for control desk.. kindly advice.
can any one tell me the formula to select the thickness of wire selection according to ampere rating
what may the reason for vector shift in a generator?
How to calculate transformer capacity requirement for a project site?
Why do we give DC excitation to AC Synchronous motor??
9 Answers Lance, MBM, Polycab,
How do i right a ladder diagram that has 1 actuator that performs a full stroke followed by a half stroke
write down the formula of cable size in RM if current is 50Amp.
hot water tank,top element 240v across,the bottom 120v across,why?
what is the resultant phase shift in a 3 phase power system including neutral if on or more phases gets grounded or short circuited. kindly explain in detail for the reasons...