Why VCB and SF6 breakers to be used in HT used by cant ACB
of higher rating to be used for 11kv and 33kv.
Answers were Sorted based on User's Feedback
Answer / gunasekaran
insulation properties of SF6 is 2-3 time than air and it is
electro negative gas so it absorb more electron at the time
of fault and normal operating condition.in acb current
chopping is occur it is will make arc between the breaker if
you go high voltage.in vcb vacuum is good insulator than air.
so higher voltage level we r using vcb SF6 breaker
| Is This Answer Correct ? | 24 Yes | 6 No |
Answer / mohammed amjath
In high voltage we use SF6 or VCB.Because if we go to ACB
the arc quenching will no be proper.Where as if we use vacum
or sulphur hexafloride the arc quenching will be 100percent.
| Is This Answer Correct ? | 19 Yes | 6 No |
Answer / x man
DURING SWITCHING THEY PRODUCE HIGH ARC,SO BY USING VACUM
AND SF6 THE ARC CAN BE EFFECTIVELY QUENCHED.
iF ACB can be used every were they why do we need at the
other protective devices.so every thing has purpose for the
invention.
| Is This Answer Correct ? | 23 Yes | 14 No |
Answer / baskaran.r
in an acb the distance between terminals are fixed for 415
volts. for higher voltages this need to be much larger.
there are some makes acbs are available in 3.3 kv with
increased gap to the tune of 2 feet. For higher voltages the
gap required will be very much higher.arc handling will be
impossible in higher voltages
| Is This Answer Correct ? | 17 Yes | 10 No |
Answer / deepak kumar
because in acb time required to extinguish the arc is much
more as compare to sf6 & vcb,if we use acb at higher
voltage , very large amount of heat will produced during
abnormal condition( short ckt) that will damage the acb or
complete circuit
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / kuldeep mehla
Beacuse Dielectric strength of vacuum & SF6 gas is more as compared to ACB. Therefore, for maintaining dielectric strenght to quench the arc at the same voltage level the size of ACB will be more compared to VCB & SF6. Therefore, ACB used in low tension line mostly.
| Is This Answer Correct ? | 2 Yes | 0 No |
According BIS,IEC standards in HT lines the Isc that current
is very highly making arc that arc is quenched by the SF6 or
vcb. If ACB has used the breaker contacts & cables are burn
out at Isc.so we used SF6 & vcb has used in HT lines for
safety purpose
| Is This Answer Correct ? | 2 Yes | 6 No |
What is the need of motor starter?
How to increase the specific gravity of DG batteries?
WHAT IS THESETTING CALCULATION FOR THE RELAY?
How to select a cable size according to load
whats the reletion betweet flow,pressure,head,rpm and motor rating?
In the N-series schneider reclosers. What is the difference between current during fault time and current at tripping? This appears in the Event log in an event of a trip out.
How to convert 110 volt alternating current to 12 volt direct current
What is dc current source? Differentiate between ideal and non ideal current sources?
how meger function
Is it necessary to install Lighting Arrester on both side side (i.e HT and LT) of Transformer in a transmission substation? if yes Why on both side?
Where servomechanism is used?
what is the thumb rule for determination resistance of resistor?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)