What is the difference between MCB and Earth MCB? What is
the working principal of MCB?
Answers were Sorted based on User's Feedback
Answer / mandeep kumar
Mcb is used in protection against shortcircuit & Overload
current where Earth MCB is used for leakage current.We may
say leakage current as Residual current.Residual means
difference of two currents.MCB works on the principal of
Cantilever Principal & Electromagnetic Induction .
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / avinash
MCB means Miniature Circuit Breaker, because it is a compact circuit breaker for domestic use.
Earth MCB are of two types: ELCB - Earth Leakage Circuit Breaker in which current flowing through the Earth wire trips the CB (Circuit Breaker) to OFF.
The other type is RCCB - Residual Current Circuit Breaker, in which imbalance of currents going in and coming out, causes CB to trip. This is more expensive and more sensitive and more protective of human life. Imbalance of the IN and OUT currents means it is flowing through something else (maybe human body) and must be tripped OFF.
| Is This Answer Correct ? | 0 Yes | 0 No |
How to detect voltage vector shifting in interconnection protection.
what is the difference between control transformer and Potential transformer (PT)?
In ACS 1000 drive we are using 12 pulse converter,why don't use 3 pulse converter.
State nyquist stability criterion.
a motor's measured current is 45amp,whereas the rated current is 38 amps but still it is running ,how?
What is use of reactor..how it is help ful in electrical system .....brief explain
How to choose primany and secondary side MCB
how is find out kwh step by step
State the methods of improving power factor?
In liquid rotor starter how PH valve should be maintained.
How to Make relay co ordination chart for a Electrical power distribution of a plant
I have 4 DG set with 1500KVA rating. system breakers are 11KV & alternator are 415 Volts. Between alternator & breaker one stepup transformer used. i want to Know what is max. resistance for body earthing & 415 & 11KV V Neuteal earthing. my fault current is 14 times for 2 sec.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)