What is the difference between MCB and Earth MCB? What is
the working principal of MCB?
Answer Posted / mandeep kumar
Mcb is used in protection against shortcircuit & Overload
current where Earth MCB is used for leakage current.We may
say leakage current as Residual current.Residual means
difference of two currents.MCB works on the principal of
Cantilever Principal & Electromagnetic Induction .
| Is This Answer Correct ? | 5 Yes | 0 No |
Post New Answer View All Answers
pls tell what are doing the three phase motor star and delta connetion with circuit diagram and control wiring .
In ups static switch if i gives the supply at output end it will open the circuit in stactic switch or not if it will open then how it operates.
what is the effect of un-synchronized power.
Pl.brief me any electrical major fault you have rectified.
how to calculate the power factor when instantaneous voltage and current has harmonics in it ?
what are the different methods for the starting of a synchronous motor.
how brushed dc motor operating ?
The SFC of an engine is 0.25 kg/kW hr. when the fuel used has a calorific value of 36000 kJ/kg. the thermal efficiency of the engine is
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
Give two basic speed control scheme of dc shunt motor?
why we r not earthed Control cable of C.T. terminals
Why arc quenching is used in Diode ?
Name one of major transformer company in KSA ?
write a program that prints prime numbers from 1-20 in digonal form
Do u know any one? how to find out in motor rated amps? formula?